SmartPins Duty Cycle measurement - Page 2 — Parallax Forums
2»
  • evanhevanh Posts: 17,313
    It may not update Z at all until expiry.
  • jmgjmg Posts: 15,200
    edited 2016-04-21 22:31
    evanh wrote: »
    jmg wrote: »
    If software reads one, then possibly the other changes, inside that reading aperture, then you have bad data.
    Standard trick is four quick reads instead of two: Read the "frequency" Z accumulator first then the "duty" Z accumulator (First pair of readings), and reread both in same order (Second pair of readings). Compare the two frequency readings. If they're the same then first pair is valid, if they're different then second pair is valid.
    That may 'mostly' work on a normal MCU, with fast SFR access, and slow PinIn values, but the P2 has a read time that is long, relative to the possible input frequency, which could be up to 80MHz.
    evanh wrote: »
    That's why I've suggested the Hold Until Read action, that allows many-pin (re) init, and then you can read the captured values from many pins.
    The results will be held indefinitely at end of expiry. Nothing extra needed.
    Hopefully you are right, & Chip has covered all use modes, nothing extra needed, however I'll reserve judgement until Chip gives more details.
    Right now, the updates only occur at the conclusion of the measurement. Then, a new measurement is automatically started.
    edited 2016-04-22 05:14
    Hmm.., I think that rather limits the use, to where users know X in advance, which is not always the case.
    Certainly not the case in Instrumentation and Testers.
    What happens in the X=0 case ?
    I was hopeful that X=0 would pass the 'control baton' to Software, allowing multiple pin, same SysCLK captures, but on SW paced request.(usually those requests are quite slow - 1~1000 milliseconds )
    Addit: Can you give an example of use ?
    I'm unclear on how one X, in one PinIn, paces two Pin's capture - did you add some cross-links to do that ?
    Or does the user load 2 X's ? that means X needs separate Clock mux, as pins may be measuring dT or dC ?
    jmg wrote: »
    The smart pins are not aware of each other. You just configure them with the same X and they will report, in unison, via IN, when they are done, with updated Z's ready to read.
    So that means the A-Field sets the Z clock, and the B-field sets the X clock source ?
    What happens when the user loads X=0 ? Can that give the Software control method ?
    edited 2016-04-22 06:46
    jmg wrote: »
    Well, the way I've thought about it, you would point both smart pins' A-inputs to the same pin. You would release them from reset at the same time. They would both run until X cycles had come in. One smart pin accumulated total SysClk cycles and the other accumulated total highs. They both started at the same time, and waited for the inital rise to start counting off subsequent rises. They both stopped on the Xth rise. One has time, the other has highs, both readable via PINGETZ.
    If the Signal is Hi then they start, is that first partial high counted ?
    I'm not sure how that Pincell knows to wait for the first _/= before starting ?
    I think the advice then has to be to discard the first reading, after a X-value change ?
    Also, is both stopped the right wording ? I thought this was a capture on X.TC ? - that does not stop anything, but repeats the capture on every X.TC ?
    More general software support for only X-forced captures, is going to need some extra range-finding code, a cost in both code size and time.
    jmg wrote: »
    When they are both released from reset (DIR rises), they both wait for the initial rise on their A-input (same pin). Then, they both set their Z registers to $00000001. One pin counts highs, while the other always increments. When the Xth rise on the A-input thereafter comes in, they both output their Z registers and raise IN. Then, a new count is underway, starting both pins' Z registers from $00000001.
    We just don't have enough flops in the smart pins to make this auto-ranging, as intermediate counts would have to be buffered before being accumulated into the main counts upon A-rise if the timeout hadn't occurred, yet.
    That is why I believe the PinCell needs the (missing?) Software Mode, (when X=0?)
    Instead of needing any auto-ranging flops, you manage the general case with a Software minimum measurement time*, and then the PinIn frequency auto-scales itself.
    Commercial reciprocal counters, do not have a range-set step, because they use Software minimum measurement time mode.
    High frequencies give more PinIn Cycles and lower frequencies give less, and the SW measurement time determines the digits of precision.
    * The actual exact measurement time, is set by the nearest-round-up-whole-cycle of PinIn.
    edited 2016-04-22 19:28
    jmg wrote: »
    I finally see the light!
    I understand now about a minimum acquisition time, and running past that, until the next (last) cycle edge of the input is registered.
    There are FOUR things that must be tracked:
    1) countdown for the minimum acquisition time
    2) number of system clocks needed to get from the first input edge, past the minimum acquisition time, to the last input edge
    3) number of highs counted during (2) - this is for duty
    4) number of input cycles counted during (2) - this is for frequency
    It will take THREE smart pins to do a complete frequency+duty acquisition. Each will have to track (1) from above, along with one of the other three.
    I'm on it.
    edited 2016-04-22 19:51
    jmg wrote: »
    4) number of input cycles accumulated during (2) - this is for frequency
    Yup, pretty much nailed it :)
    The beauty of Multi-pin co-operation, is someone can use THREE smart pins, if they want to do a complete frequency+duty acquisition. ( That little side-ways Pin Mux feature, has made this very powerful indeed )
    If they just want Precision Frequency, or Duty, they need use only 2 (,4,6,8,10 for Multiple channels).
    Of course, once you tell someone they can have both, they start thinking about Sensor designs that can isolate over one wire, and convey two lots of Precision Analog information - One encoded in Duty, the other encoded in Frequency.
    I'm on it.
    Look forward to seeing what comes out :)
    The way I see it, item 1) does not have to be done in the Pin, that can be SW as it is a minimum acquisition time (eg 10ms, 100ms), ie it does not need to cost flops, you just need SW access to request capture-next-edge from many pins.
    The small detail of reset of Z to $00000001, I am only luke-warm on.
    I prefer no-reset, and using a simple difference dC, dT, as that avoids delay skew housekeeping details.
    (ie makes the hardware easier, and SW cost is minimal ).
    If the pin cell takes (say) any one of 1,2,3,4 SysCLKs to pipeline some of these actions, with a difference approach (no reset) that vanishes, as it is always the same delay. With reset, the IC designer (aka you) needs to count those SysCLKs.
    Knowing you have no SysCLK count creep, also means you can run a background average over 100, 1000, etc readings, for precision limited only by the numeric base.
    jmg wrote: »
    jmg wrote: »
    I'm on it.
    I think getting the acquisition timer out of the smart pin is good, because that might as well be done by software: start it, pass some time, stop it, and wait for the results via IN after the final A-input edge. Having the smart pins do the minimum timer is silly, because the exact time elapsed does not matter and will not be consistent, anyway - so why put a 32-bit comparator in each pin? The wrap-it-up signal can come from the B-input, which could be set to be the OUT bit, which bit can be set for all pins at once with an 'OR DIRA,##%111<<pinbase'.
    This means that each smart pin in reciprocal-counter mode can track either system clocks, A-input edges, or highs. So, there will be three sub-modes to pick which measurement you are taking.
    Agreed.
    I think the additional option of your X-counted captures is useful (if that has low logic count) as that is broadly equivalent to Microchips Capture prescalers, and some users will understand that.
    The more general software-paced you describe above, is better for libraries and general use.
    That was why I suggested using X=0 as a means to flip X-Counted or SW-Paced, but SW-Paced alone, is fine.
    X-Counted may be useful in some special cases, where Rate-Multiplier type PWM or sub-cycle jitter is used, and you know there are frames of 256, 1024 cycles, (or whatever).
    One example: A P2, or other small MCU, sends PWM at 80M/2^12 = 19.53125 KHz, and also dither modulates that, in 256 frames.
    X=256 would give a ~20 bit result(12+8), at 76.29 Hz reading rates.
    A small part like EFM8LB1, could send multiple 14b ADC results over a simple PWM link.
    jmg wrote: »
    Agreed.
    I agree. There could be some X-prescaler modes, and then if X=0 we use the B-input to start and stop the acquisition.
  • jmg wrote: »
    And, you just re-invented QAM.
    Just externally filter the signal and apply the Goertzel. Direct readout of frequency deviation (Phase) and duty (Amplitude). Use them separately, or develop a classic N bit by N bit constellation for data transfer.
    edited 2016-04-28 11:19
    I finally got all the special measurement modes in the smart pin worked out. They are modes %10011..%10111:
    MMMMM	Description				OUT	Inputs		Pattern
    00000	OUT (default)				OUT	A,B		<none>
    00001 *	DAC noise				OUT	A,B		output-update-repeat
    00010 *	DAC 16-bit dither, noise		OUT	A,B		output-update-repeat
    00011 *	DAC 16-bit dither, PWM			OUT	A,B		output-update-repeat
    00100 *	X pulse(s)				drive	-		wait-output-repeat
    00101 *	X edges					drive	-		wait-output-repeat
    00110 *	NCO freq				drive	-		output
    00111 *	NCO duty				drive	-		output
    01000 *	PWM triangle 16:16			drive	-		output-update-repeat
    01001 *	PWM sawtooth 16:16			drive	-		output-update-repeat
    01010 *	PWM SMPS, A=V, B=I			drive	A,B		output-update-repeat
    01011 *	A-B quadrature encoder			OUT	A,B		measure-report-loop
    01100 *	A-high inc				OUT	A,B		measure-report-loop
    01101 *	A-rise inc				OUT	A,B		measure-report-loop
    01110 *	A-high inc, B-high dec			OUT	A,B		measure-report-loop
    01111 *	A-rise inc, B-rise dec			OUT	A,B		measure-report-loop
    10000 *	time A-state periods			OUT	A,B		time-report-loop (!sign = state)
    10001 *	time A-high periods			OUT	A,B		time-report-loop
    10010 *	time X A-highs				OUT	A,B		time-report-loop
    10011 *	for X periods, count time		OUT	A,B		time-report-loop
    10100 *	for X periods, count states		OUT	A,B		time-report-loop
    10101 *	for periods in X+ clocks, count time	OUT	A,B		time-report-loop
    10110 *	for periods in X+ clocks, count states	OUT	A,B		time-report-loop
    10111 *	for periods in X+ clocks, count periods	OUT	A,B		time-report-loop
    11000 *	USB host, low-speed			drive	A,B		receive-repeat
    11001 *	USB host, full-speed			drive	A,B		receive-repeat
    11010 *	USB device, low-speed			drive	A,B		receive-repeat
    11011 *	USB device, full-speed			drive	A,B		receive-repeat
    11100 *	B-clk tx				drive	B		transmit-repeat
    11101 *	B-clk rx				OUT	A,B		receive-repeat
    11110 *	async tx				drive	-		transmit-repeat
    11111 *	async rx				OUT	A,B		receive-repeat
      * DIR from cogs: 0=reset, 1=start; IN to cogs: 1=done; 'PINACK pin' clears done
    edge selection via PINSETY for modes 10011..10111
    00 = A-rise to B-rise
    01 = A-rise to B-edge
    10 = A-edge to B-rise
    11 = A-edge to B-edge
    You can select what constitutes a period via PINSETY for these modes. A period is not necessarily a cycle, but an A-to-B event, where B can be A, also. The 'state' that can be counted in modes %10100 and %10110 is the leading edge of the A-input which starts a period. Periods can now overlap if the trailing B-input edge (may be same as A-input) is coincident with the leading A-edge.
    I'll get these documented and into the next release.
    edited 2016-04-28 12:59
    Jmg, these special counter modes work great! I realized that there WAS sufficient logic to set a minimal sample timer that repeats automatically, like in other modes. You just tell it how long to look and it will count up whole periods until the timer runs down to 1. Then, it just waits for the last trailing edge to wrap up the measurement. And it can even handle coincident trailing and leading edges, making cycle counting contiguous. Really nice! Thanks for bringing this up (and up, and up...). It's very nice to have in the smart pin. It only added several ALMs per pin.
    Since I had a spare slot, I also added a new mode (%10010) which times how long it takes to register X high samples on the A input. That ought to be good for something.
    Nice! Covers muchly.
    Sounding great ! :) I was prepared for the COG to do at least some of the slower work... ;)
    ( Sorry to play the squeaky wheel, but I could see that the Smart Pin cell was almost able to do this before...)
    Does this still clear Z on capture ?
    Can you post code examples used to test each of these modes, so others can stretch them around ?
    One easy test I can think of, is to connect a couple (or 3) GPS modules, and measure the 1pps on each.
    Set the Min-time to 0.5s, 13s, 50s
    Then, also measure time-interval A-B between modules, to check the 1pps edge alignment jitters.
    You should get 12.5ppb, ~1ppb, 0.25ppb LSBs
    Isn't that one of the modes needed for Duty Measurement ?
    See also the thread on fast PWM
    http://forums.parallax.com/discussion/comment/1373564/#Comment_1373564
    Here, dither over some frame count, gives higher average precision.
    To get best results of measuring such a frame-dithered PWM signal, if the user knows beforehand how many cycles the frame is, they can set the capture counts to be a multiple of that.
    Capture then gets all the information, every time, with no partials, for best precision.
    On the topic of Duty-Cycle Measurement, this new part from Infineon is nifty :
    http://www.infineon.com/cms/en/product/power/lighting-ics-and-audio-driver-ics/dc-dc-led-driver-ic-and-linear-control-solutions/CDM10V/productType.html?productType=5546d46253f65057015414dc7d576130
    In a SOT23-6? this accepts a standard, simple 0-10V, (or R) and outputs a 5mA current PWM for direct opto drive.
    Looks nice for Isolated, remote analog, to modest precisions.
    edited 2016-04-28 20:40
    This will make for some attention-grabbing demonstrations !!
    Set the Min-time to (say) 0.5s, 12.5s, 49.9s
    edited 2016-04-28 20:59
    Jmg, about clearing Z on capture...
    It does, but the increment is still added in, setting it to one. This is needed, though, since when we detect end-of-cycle, the current value of the Z register needs to be sent for the update, not Z from the next cycle, which would have been incremented (and also cleared, leaving $00000001). This all works out and gives perfect results, as output of $00000000 is never possible. For the measurement to end, some measurement had to be taken, making it always >= 1.
    Interesting idea about testing the GPS modules' jitter.
    Cool, I was just worried about the potential for missing unusual cases.
    If it tests ok in all cases, then that is great.
    Users need to be able to capture at some faster rate (say >~ 100ms) and also run a background, slower 10s or 50s accumulate.
    If there are never any lost edges, then that background accumulate is a correct answer.
    GPS should give a good way to test this, and should catch any off-by-one slip-ups.
    If you have this all working in a pin now, with minimal SW overhead, then clipping on GPS for added precision (or calibrate) becomes quite easy to do. GPS-volumed (VC)TCXO's are also remarkably cheap recently.