About a mechanical relay
Hi,
I have a 120 volts 3 amp relays.
I want to use them with 220 volts at 1 amp instead of 120 volts 3 amp.
Could be a damage ? and is it dangerous ?
I have a 120 volts 3 amp relays.
I want to use them with 220 volts at 1 amp instead of 120 volts 3 amp.
Could be a damage ? and is it dangerous ?

Comments
-Phil
That particular relay likely has a replacement that has a 220 volt rating if you wanted to change them out.
However, there might be a serious problem with the spacing or current capability of the circuit board traces.
In the circumstances it would make sense to use the existing relay to switch an external relay, either solid state or electro-mechanical, which has suitable ratings and can be mounted in a safe enclosure.
Cheers,
Link:[URL=" http://www.tianbo-relay.com/bigimg/15.pdf"] http://www.tianbo-relay.com/bigimg/15.pdf[/URL]
TUV is a testing and certification company, like UL listing:
http://www.tuv-sud-america.com/us-en/tuev-sued-america/about-tuev-sued-america
One amp at 220 volts is a maximum rating. That would be too close for comfort for me. I tend to double the ratings so I don't have to make service calls.
Also, I agree it's best to stay below maximum ratings. Always give yourself a cushion. The 250VAC rating should be okay but the 1A is just too close for comfort.
Also, without information about the circuit board ( trace dimensions, spacing and board substrate material ) that the relays are mounted on, they may in fact only be rated at a fraction of those values by the time you connect to the terminal screws.
Cheers,
What you need to do is to start with a relay that may be adequate AND derate it by the particular use. If also is important to have snubbers on the switching side of the relay to add useful life. Derating can easily be 40% reduction in current capacity. So a 5 amp relay in actual use may be used to only switch 3 amps.
Here is a wikipedia entry on relays with discussion of derating --- http://en.wikipedia.org/wiki/Relay
And here is a Pdf with more info on derating and extending useful life --- cp.literature.agilent.com/litweb/pdf/5988-6917EN.pdf
You won't get much life out of a relay by going the opposite direction and attempting operation at the 'absolute max'. Those are intended to indicate safe limits for momentary abuses.