Hello!
I want to work with the stamp plc and activate a resistive load (heating device) that uses 220ACV, as sensors I might use·some DS2760 with a more expensive thermocouple than the cable that's inclueded in the DS2760 kit. This is for some machines in my father's corporation. The only problem I have is the 24v to 220v interface which I need to be in a way that the PLC and the stamp in it is safe from any problem.
Best Regards

Manuel C. Reinhard

▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
Best Regards

Manuel C. Reinhard

Comments

  • Chris SavageChris Savage Parallax Engineering Posts: 14,406
    edited 2006-07-14 16:15
    Hello,

    ·· Connecting the 220V stuff is easy via an SSR.· Many have an input range well within the Stamp PLC.· The problem I see is connecting the one-wire device.· All I/O is isolated and you couldn't directly read the thermocouple.

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    Chris Savage
    Parallax Tech Support
    csavage@parallax.com
  • ManuelManuel Posts: 105
    edited 2006-07-15 08:11
    Why won't the optical isolation let me read data directly from the DS2760's? Isn't it still 1s and 0s?

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    Best Regards

    Manuel C. Reinhard
  • Chris SavageChris Savage Parallax Engineering Posts: 14,406
    edited 2006-07-17 14:23
    Manuel,

    ·· Here is the problem...Normally any Stamp I/O pin is bi-directional.· In industrial applications most devices are INPUT or OUTPUT.· When you optically isolate the input, it cannot be an output anymore in this configuration.· The 1-Wire protocol regarding this device requires you to send commands to it to retrieve values/information from it.· You have no way to do that currently.· Take care.

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    Chris Savage
    Parallax Tech Support