metron9metron9 Posts: 1,100
edited 2006-01-05 16:04 in General Discussion
Please confirm this is ok to do

Using the table below I calculate I can run 36 Lumileds at 320 mA using a standard 24AWG ethernet cable

AWG      Dia Inch   enclosedAmps
-----------------------------------------
24         0.020     2.1




I only need 4 wires to each device. (12V+,Ground, and two signal lines fot the electronics on board each device)
Each device will have three Lumileds in series. I will dasichain up to twelve devices so that

12V DC Voltage
Lumiled 3.5 to 4V Forward Voltage
(I will be using a current source onboard each device to hold maximum 320mA per device)

320 mA per device * 12 = 3.84 Amps

SO BY USING 2 wires for +12V and 2 wires for the Ground return I can use up to 4.2 Amps.

Two connectors on each device to dasychain 12 devices (with 3 Lumileds in series each) in parallel

▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
Think outside the BOX!

Comments

  • Robert KubichekRobert Kubichek Posts: 343
    edited 2006-01-02 17:35
    metron9 said...
    Please confirm this is ok to do

    Using the table below I calculate I can run 36 Lumileds at 320 mA using a standard 24AWG ethernet cable

    AWG      Dia Inch   enclosedAmps
    -----------------------------------------
    24         0.020     2.1
    
    



    I only need 4 wires to each device. (12V+,Ground, and two signal lines fot the electronics on board each device)
    Each device will have three Lumileds in series. I will dasichain up to twelve devices so that

    12V DC Voltage
    Lumiled 3.5 to 4V Forward Voltage
    (I will be using a current source onboard each device to hold maximum 320mA per device)

    320 mA per device * 12 = 3.84 Amps

    SO BY USING 2 wires for +12V and 2 wires for the Ground return I can use up to 4.2 Amps.

    Two connectors on each device to dasychain 12 devices (with 3 Lumileds in series each) in parallel

    Don't forget to figure in the voltage drop in the length of wire you will be using. To be safe, I would double the wires in the power loop.
    If I remember right, the optimum specs for a Luxeon is 3.6 v at 350ma, using suitable heat sinking.. A 12v supply using individual regulators for each string of 3 might not be enough overhead if you factor in the loss you get ( regulator, wire length )..

    Bob N9LVU scool.gif
  • PJAllenPJAllen Banned Posts: 5,065
    edited 2006-01-02 17:49
    metron9,

    · Have you turned on one of these yet?· I don't know what your level of expertise is, but I suggest a step-by-step approach instead of going whole-hog from the get-go to be followed by the "nothing works... and I burn my finger when I touch..." Reply post.· Does that make sense?



    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    When you get 1st Place in the "Darwin Awards", you're a Winner & a Loser.
  • Robert KubichekRobert Kubichek Posts: 343
    edited 2006-01-02 18:04
    PJ Allen said...
    metron9,


    Have you turned on one of these yet? I don't know what your level of expertise is, but I suggest a step-by-step approach instead of going whole-hog from the get-go to be followed by the "nothing works... and I burn my finger when I touch..." Reply post. Does that make sense?

    How true, I have trashed some regular leds by using wrong resistor value (math error)! shocked.gifshakehead.gif
    I used some old cpu heatsink/fans when I "experimented" with my 5W units, worked like a charm!!! smilewinkgrin.gif

    Bob N9LVU scool.gif
  • metron9metron9 Posts: 1,100
    edited 2006-01-02 18:09
    I have one I am working with now and waiting for the mailman to bring me a dozen or so for testing.
    Yes I will be making just 2 devices to start with.

    WHen you say double the wires you mean use 4 wires instead of 2?

    Any suggestions on 4 wire connectors that would work for this application?

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    Think outside the BOX!
  • Robert KubichekRobert Kubichek Posts: 343
    edited 2006-01-02 18:24
    metron9 said...
    I have one I am working with now and waiting for the mailman to bring me a dozen or so for testing.
    Yes I will be making just 2 devices to start with.

    WHen you say double the wires you mean use 4 wires instead of 2?

    Any suggestions on 4 wire connectors that would work for this application?

    Sure, use the same connectors found on computer power supplies to HD/CD/DVD's smilewinkgrin.gif

    Bob N9LVU scool.gif
  • metron9metron9 Posts: 1,100
    edited 2006-01-02 18:40
    " Sure, use the same connectors found on computer power supplies to HD/CD/DVD's "

    Yes I am thinking of these connectors as well however they do not have a positive lock clip on them
    I am looking for off the shelf wires/connectors if possible. We were using the regular rj11 phone connectors when the devices used only a few LED's each but now that we have gone high power in the design the wires and connectors are on the front burner so to speak now so we are just exploring options.

    We are looing at these as well: http://www.action-electronics.com/ampcpc.htm

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    Think outside the BOX!
  • Alan BradfordAlan Bradford Posts: 172
    edited 2006-01-03 01:13
    Hi Robert,

    You not only need to look at the ampacity of the wire, but the temperature rating of the insulation.
    You can safely pass lots of amps through a conductor until it melts!!! But you have to think of the insulation rating.

    I dont know about the type of cable you are thinking about, but most network cable is not rated to take much internally generated heat. It is a good size conductor, so there will not be much signal loss over long runs.
    The resistance is given as ohms per unit distance. The longer the cable the more heat you will generate.

    Here is a link for single conductor wires and the safe ampacities.

    www.alphawire.com/PAGES/383.CFM

    You have to derate the wire for multiple conductors, and low temperature rated insulation.

    The money you save by using the wrong type of wire you will spend in making the power supply big enough to light the leds after heating up the wire. Remember the losses come first!

    Alan Bradford
    Plasma Technologies
    www.plasmatechnologies.com
  • PJAllenPJAllen Banned Posts: 5,065
    edited 2006-01-03 01:21
    I think he's figuring on using CAT-5 (he says they were using RJ-11 connectors previously.)· Depending on the type, it may melt, BUT if it's "plenum" then it won't catch fire.· devil.gif

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    When you get 1st Place in the "Darwin Awards", you're a Winner & a Loser.
  • Robert KubichekRobert Kubichek Posts: 343
    edited 2006-01-03 01:31
    Alan Bradford said...
    Hi Robert,



    You not only need to look at the ampacity of the wire, but the temperature rating of the insulation.

    You can safely pass lots of amps through a conductor until it melts!!! But you have to think of the insulation rating.



    I dont know about the type of cable you are thinking about, but most network cable is not rated to take much internally generated heat. It is a good size conductor, so there will not be much signal loss over long runs.

    The resistance is given as ohms per unit distance. The longer the cable the more heat you will generate.



    Here is a link for single conductor wires and the safe ampacities.



    www.alphawire.com/PAGES/383.CFM



    You have to derate the wire for multiple conductors, and low temperature rated insulation.



    The money you save by using the wrong type of wire you will spend in making the power supply big enough to light the leds after heating up the wire. Remember the losses come first!



    Alan Bradford

    Plasma Technologies

    www.plasmatechnologies.com

    You have the wrong person here, I was replying to "metron9".... yeah.gif

    And if he uses say 3 or more wires on slupply and on ground legs, based on his calculations, he should be safe. turn.gif


    Bob N9LVUscool.gif
  • metron9metron9 Posts: 1,100
    edited 2006-01-03 06:42
    We don't have to run 12 per string we could spec 6 units maximum and use 2 connector lines on the supply box
    The length of wire between the units will be at most 6 feet
    The units will only be used at most 50% duty cycle each and it would be impossible to light all of them at once.
    But I still want to make sure if for some reason they all did hold in the on position it would take the heat.

    So with that, I will continue and run some tests.

    I see one of the cat-5 cables I have has a 75c printed on the wire.

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    Think outside the BOX!
  • PJAllenPJAllen Banned Posts: 5,065
    edited 2006-01-03 13:44
    How about a video -- when you turn it On the first time (you have to be in the field of view, of course)?· devil.gif
    ·
  • knightofoldcodeknightofoldcode Posts: 233
    edited 2006-01-04 06:04
    PJ Allen said...
    I think he's figuring on using CAT-5 (he says they were using RJ-11 connectors previously.) Depending on the type, it may melt, BUT if it's "plenum" then it won't catch fire. devil.gif

    This is actually incorrect. It can still catch fire. The only thing that plenum states is that it won't produce "as much" smoke as pvc coated cables. Exactly how much isn't known. [noparse];)[/noparse] (At least to me, anyways.)

    expertanswercenter.techtarget.com/eac/knowledgebaseAnswer/0,295199,sid63_gci1104930,00.html said...

    PVC, or PolyVinylChloride, refers to the coating of the cable jacket. If you have riser or plenum rated cables, they are slower to burn and produce less smoke than PVC and are rated to be installed in plenum areas (any area with return air).

    Knight.

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    -=-=-=-=-=-=-=-=-=-=-=-=-=-=-=--=-=-=-=-=-=-=-=-=-=-=-=-
    This message transmitted with 100% recycled electrons.
    -=-=-=-=-=-
    Gravity doesn't exist. The Earth sucks.
    -=-=-=-=-=-
    Make a man a fire, and he will be warm for the night.
    Light the man on fire, and he will be warm for the rest of his life.
    -=-=-=-=-=-=-=-=-=-=-=-=-=-=-=--=-=-=-=-=-=-=-=-=-=-=-=-
  • knightofoldcodeknightofoldcode Posts: 233
    edited 2006-01-04 06:11
    As for high amperage connecters, I've been pleased with the Anderson Power Poles. Digikey has the molex version of these connectors, but they are genderless, and have ratings of 15/30/45 amp (I assume at 12V, since they are designed for automotive), and higher. The best part is that they are genderless. I use them in my work truck for connecting things such as inverters, trailers, lighting, and I use the higher version 200amp for connectors for jumper cables.

    www.powerwerx.com/

    If you're looking for a smaller profile, I use the old keyboard style connectors. I'm not sure the amperage ratings, but they are fairly high, probably at least 40-50 watts. Digikey, Mouser, Jameco, just about everyone carries them for decent prices. For this kind of stuff just look around in the digikey and mouser catalogs, there are TONS of connectors with any size power rating needed.

    Knight.

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
    -=-=-=-=-=-=-=-=-=-=-=-=-=-=-=--=-=-=-=-=-=-=-=-=-=-=-=-
    This message transmitted with 100% recycled electrons.
    -=-=-=-=-=-
    Gravity doesn't exist. The Earth sucks.
    -=-=-=-=-=-
    Make a man a fire, and he will be warm for the night.
    Light the man on fire, and he will be warm for the rest of his life.
    -=-=-=-=-=-=-=-=-=-=-=-=-=-=-=--=-=-=-=-=-=-=-=-=-=-=-=-
  • metron9metron9 Posts: 1,100
    edited 2006-01-05 16:04
    I have made a prototype, The light intensity will not be a problem at 200mA per unit at 18V. (actually 2 diode drops or 16.6V is what we will be using)

    So 16.6 * .2A = 3.32 Watts Times 10 = 33.2 watts On the first 5 foot length of wire to the first unit and 3.32 watts less for each of the remaining connections.

    We will use 2 wires each for ground and the 16.6V feed

    At no time will all of the units receive full power at the same time. I estimate less than 20% of the power will be used on average so this part is done.

    I did smoke some resistors (1/4 watt) when my wires from my dual 9V batterys crossed and shorted, (note to self, tape bare wire ends on battery when testing stuff and buy some higher wattage small resistors)

    We will be using a self resetting fuse on the main power distribution for short circuit protection.

    Hmmm, guess I will add another led and pnp transistor on the power distribution box to show short circuit condition....

    ▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔