Motor Control with 4-20mA signal
bhaan
Posts: 37
I am trying to control a motor with a 4-20mA signal.· I am aware of the PWM feature of the BS2, however that is not a "true" analog signal and I would rather use other methods.· On the schematics of the actuator I am trying to control it shows "y+" and·"y-"· terminals that I have to connect to.· Can I use a a digital Potentiometer to control the actuator, and if so, is the "y-" terminal supposed to be connected to ground?· I do not have a great deal of experience with electronics so this is a little confusing to me.· Any ideas or advice would be greatly appreciated.
Thanks,
Brian
I have a pdf of the technical specs of the actuator, if it would help I could post the pdf.
Thanks,
Brian
I have a pdf of the technical specs of the actuator, if it would help I could post the pdf.
Comments
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
My circuit board in the motor is the: AGA56.41A17
The bottom of page 9 and then page 10 has the actual schematics.· The 4-20mA signal is the one I have to use and is the part I am not sure how to do.
That thing looks like a honeywell clone, complete with all the cam and micoswitch nonsense. If you’re looking for better actuator with programmable limits, signals check out the MFT series from Belimo. www.belimo.com. If you need some pm me, I work for a platinum dealer and can good prices.
http://www.maxim-ic.com/appnotes.cfm/appnote_number/807 - see figure 6
http://www.maxim-ic.com/appnotes.cfm/appnote_number/722
http://www.discovercircuits.com/PDF-FILES/NewPDF/CURRENTSOURCE1.pdf - replace 10k pot with a digital?
http://www.elecdesign.com/Articles/Index.cfm?AD=1&ArticleID=9944 - Precision Programmable Current Sources Use Digital Pots
Post Edited (Orion) : 7/2/2005 5:01:51 PM GMT
·
Post Edited (Orion) : 7/2/2005 5:41:31 PM GMT
I am controlling a test furnace to follow a specific temperature curve and send all·the data to·a PC. ·I have already written software to communicate with the stamp and save all aquired data to a spreadsheet, but I still have to calibrate the PID part of the software after I get everything figured out.· I'll have the software do all calculations and then have it determine a setting to send to the BS2 so it can control the actuator.·
Would D/A converters be the answer to sending my 4-20mA signal?· I was looking for one·at maxim-ic but I was a little confused with all the different options they offer.
Paul said something about output impedance earlier, I am unclear on what output impedance is?·
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
http://www.discovercircuits.com/PDF-FILES/NewPDF/CURRENTSOURCE1.pdf
Another option, using a transducer card like this one (PWA-2A)
http://www.kele.com/olcat/OT8/PWA.pdf
to convert from a digital pulse to 4-20ma. That one will drive up to a 650ohm load. I have used these many times to interface to 4-20ma devices. The pwm signal they accept has a long cycle time, so a stamp could do other times in the mean time. Also, I believe this card holds its output when no input signal is present, stamp could signal once and continue. That is something I could test next week if we have one in stock, and you’re interested.
I still think it would be better to find a simple circuit that you could generate the signal with a digital pot or DAC. Why have controls driving controls.....
BTW My company also is a Kele dealer and can get you a big cut off the list price.
http://www.chipdocs.com/pndecoder/number/694.html
Check out the AD694 - http://www.analog.com/UploadedFiles/Data_Sheets/390142776AD694_b.pdf
This could be driven with a 0-2v or 0-10v signal to drive 4-20ma current loop.
Paul,
My though on the impedance figure on page 24 is they are talking about the input of the actuator. i.e. the input is going to look like a <=300ohm resistor in the loop to the transmitter.
Anyway I have a digikey order I'm working up, and I'll add a AD694 and give it a try.
Post Edited (Orion) : 7/3/2005 5:22:38 PM GMT
$10.00 on digikey
Do you see any problems with using it?
No, it may not work though.
Is the output impedance in range?
Output impedance is not even in the ballpark, though I searched all over for something that was and found nothing yet.
In eight years of commercial controls work and I have never had much of a problem with current loops and compatibility. Two main things to know: what sources/sinks the loop power and to min/max voltage level of the devices. I think the datasheet of your actuator is talking about the input impedance and not the output. It wouldn't be the first time I was wrong though. I ordered a few of the AD694s and will try them on some devices we have at our shop. They should be in my hands this weekend unless the holiday screws things up. If I get it working I'll post you a schematic, and you can give it a try. The only thing I have seen toast sensors and controllers is two sourcing devices on the same loop. I wouldn't worry about smoking something. Worst case you may have a ten dollar IC that takes days to drive your actuator from open to close. At that point it may be easier to change out the input card on the actuator for one that will take a voltage input.
http://www.advantech.com/products/Model_Detail.asp?model_id=1-D6FJV&bu=#
For now, I think I·am going to try to get some components to test the circuit Paul posted, although I can't seem to find anywhere to buy the TL032 ampliphiers shown.· Digikey doesn't stock that item.· Orion, let me know if your test with the·AD694 works.
I found digkey has the TL032 in 8-DIP and 8-SOIC.
I finally wired up Paul's circuit and it works great, but I'd like to not have to use the PWM command so that I don't have to loop it.
Post Edited (bhaan) : 7/13/2005 2:45:00 PM GMT
The circuit Orion posted using the AD694 has a high impeadance input for the 0-2V input signal. This means the output impedance of the voltage source isn't a big issue, so you can use a digipot to set the input voltage.
After re-analyzing the EDN article, I am fairly certain that removing the 4.7 µF capacitor from the input of the circuit will adapt the circuit for use with an analog input for the control circuit, enabling use of a digipot. Actually come to think of it, you can use an analog signal for the input of the circuit as it exists. This is because the 4.7 µF capacitor integrates the PWM signal into an analog voltage. If you supply a constant voltage in (not rapidly changing) the capacitor has no effect on the input voltage (capacitors "resist" changes in voltages across its terminals by storing or releasing electrons from it's plates, if the voltage across the terminals is not changing, the charge on the capacitor stays the same and therefore does not affect the voltage on it's positive terminal), it is just fed straight to the op-amp. The only effect of the 4.7 µF capacitor when using an analog input is when the input voltage is changed the capacitor causes the input voltage to change more slowly. This will cause the output current to also change more slowly. This may be a desired quality for you, it depends on how the device your controlling reacts to a rapidly changing input current. Making the capacitor value smaller will cause the output to change more quickly, increasing it will cause the output to change more slowly.
Post Edited (Paul Baker) : 7/13/2005 3:16:12 PM GMT
·
That actuator is pretty big so I’m assuming that it’s a gas valve on a large furnace.· Natural gas can be a very impressive force if misused.· Is this valve part of a piece of a package unit?· If so you best understand how all the safeties and wiring they have in place before you take control of the valve.· Boilers can crack if put to a high rate of fire and the water is too cold,· furnace heat exchangers can crack/catch fire·releasing carbon monoxide into the air.· Just be careful and understand how the equipment operates before you change its control.· If any safeties trip on that unit, your valve should fail close, even if there is a 2-position valve before it.· Gas valves can stick.
·
Post Edited (bhaan) : 7/14/2005 1:34:09 PM GMT