Serial Output Error
When running RealTerm, the output·of the code produces strings of decimal numbers of the correct length.· However, the output strings to not match·the string of decimal numbers specified inside the code for a given word.·
What could be causing this to·happen?
Beau Schwabe - Mask Designer III
National Semiconductor Corporation
Latest Company News
(Communication Interface Division)
500 Pinnacle Court, Suite 525
Mail Stop GA1
Norcross,GA 30071
You asked what could be causing this to happen. This was the first thing that I thought of that might be a culprit.
A quick look at "realTerm" and the option to invert the data is NOT the same as inverting the RS232 serial data leaving the SX / entering the PC
realterm.sourceforge.net/
Latest Company News
Mail Stop GA1
Norcross,GA 30071
Post Edited (Beau Schwabe) : 4/8/2005 8:30:12 PM GMT
Ok... A serial BYTE is actually 10-bits. You have 8-Data bits that compose a Byte, and you have a START and a STOP bit
that make up the other 2-bits totaling 10-bits.
The inversion that I am suggesting is in the "BaudMode" setting as part of the SEROUT routine. When this is set, not only are the DATA
bits inverted (same as the 'not w command' or flipping this in the realTerm) BUT, the STOP and START bits are also inverted.
Now, you mention that you have different baud speeds. This needs to be corrected first! you should have the same Baud setting for
everything within the SX and within realTerm.
Latest Company News
Mail Stop GA1
Norcross,GA 30071
I still think you are going to have problems mixing different baud modes.
It is important to work out a common denominator that you can transmit and receive data with.
Also, I assume you are programming on an SX.. Are you using SX/Basic or SX/Assembly for your programming?
Latest Company News
Mail Stop GA1
Norcross,GA 30071
Jim
But, now we get extra numbers before the output that is supposed to correspond to the values for welcome.
Intended output: 84,147,131,145,195,136,140,255,0
Actual output: 0 140 140 112 124 31 0 12 28 31 56 130 168 77 131 145 195 136 140 255
Here is the new code, with the problem fixed.
LIST Q = 37 ;disables truncation errors
device SX28,oschs2,turbo,stackx,optionx
freq 50_000_000
IRC_CAL IRC_FAST
; ** Baud Rates for UART 1 **
U1B1200 ;baud rate of 1.2 Kbps
; ** Baud Rates for UART 2 **
U2B9600 ;baud rate of 9.6 kbps
id '2UART VP' ;
reset resetEntry ; set reset vector
Macro's
; Macro: _bank
; Sets the bank appropriately for all revisions of SX.
; This is required since the bank instruction has only a 3-bit operand, it cannot be used to
; access all 16 banks of the SX48/52. FSR.7 (SX48/52bd production release) needs to be set
; appropriately, depending on the bank address being accessed. This macro fixes this.
; So, instead of using the bank instruction to switch between banks, use _bank instead.
_bank macro 1
noexpand
bank \1
expand
clrb fsr.7
noexpand
endm
; Macro: _mode
; Sets the MODE register appropriately for all revisions of SX.
; This is required since the MODE (or MOV M,#) instruction has only a 4-bit operand.
; The SX28AC use only 4 bits of the MODE register, however the SX48/52BD have
; the added ability of reading or writing some of the MODE registers, and therefore use
; 5-bits of the MODE register. The MOV M,W instruction modifies all 8-bits of the
; MODE register, so this instruction must be used on the SX48/52BD to make sure the MODE
; register is written with the correct value. This macro fixes this.
; So, instead of using the MODE or MOV M,# instructions to load the M register, use
; _mode instead.
_mode macro 1
noexpand
expand
mov m,#\1 ;loads the M register correctly for the SX18AC, SX20AC
;and SX28AC
noexpand
endm
; INCP/DECP macros for incrementing/decrementing pointers to RAM
; used to compensate for incompatibilities between SX28AC and SX52BD
INCP macro 1 ; Increments a pointer to RAM
setb \1.4 ; If SX18 or SX28AC,keep bit 4 of the pointer = 1
; to jump from $1f to $30,etc
endm
DECP macro 1 ; Decrements a pointer to RAM
clrb \1.4 ; If SX18 or SX28AC, forces rollover to next bank
dec \1 ; if it rolls over. (skips banks with bit 4 = 0)
setb \1.4 ; Eg: $30 ---> $20 ---> $1f ---> $1f
; AND: $31 ---> $21 ---> $20 ---> $30
endm
; Error generating macros
; Used to generate an error message if the label is intentionally moved into the second page.
; Use for lookup tables.
tablestart macro 0 ; Generates an error message if code that MUST be in
; the first half of a page is moved into the second half
if $ & $100
ERROR 'Must be located in the first half of a page.'
endif
endm
tableEnd macro 0 ; Generates an error message if code that MUST be in
if $ & $100
endif
endm
Memory Organization
Data Memory address definitions
; These definitions ensure the proper address is used for banks 0 - 7 for 2K SX devices
; (SX28) and 4K SX devices (SX48/52).
global_org = $08
bank0_org = $10
bank1_org = $30
bank2_org = $50
bank3_org = $70
bank4_org = $90
bank5_org = $B0
bank6_org = $D0
bank7_org = $F0
Global Register definitions
; NOTE: Global data memory starts at $0A on SX48/52 and $08 on SX18/20/28.
org global_org
flags0 equ global_org + 0 ; stores bit-wise operators like flags
; and function-enabling bits (semaphores)
VP: RS232 Receive
rs232Tx1Flag equ flags0.0 ;indicates that UART1 is transmitting if set or not transmitting if reset
rs232Tx2Flag equ flags0.1 ;indicates that UART2 is transmitting if set or not transmitting if reset
rs232Rx1Flag equ flags0.2 ;indicates that UART1 has received a byte if set
rs232Rx2Flag equ flags0.3 ;indicates that UART2 has received a byte if set
isrTemp0 equ global_org + 1 ; Interrupt Service Routine's temp register.
; Don't use this register in the mainline.
localTemp0 equ global_org + 2 ; temporary storage register
; Used by first level of nesting
; Never guaranteed to maintain data
localTemp1 equ global_org + 3 ; temporary storage register
; Used by second level of nesting
; or when a routine needs more than one
; temporary global register.
localTemp2 equ global_org + 4 ; temporary storage register
; Used by third level of nesting or by
; main loop routines that need a loop
; counter, etc.
RAM Bank Register definitions
; Bank 0
org bank0_org
bank0 = $
; Bank 1
org bank1_org
bank1 = $
rs232TxBank = $ ;UART Transmit bank
rs232Tx1High ds 1 ;High Byte to be transmitted
rs232Tx1Low ds 1 ;Low Byte to be transmitted
rs232Tx1Count ds 1 ;counter to keep track of the bits sent
rs232Tx1Divide ds 1 ;xmit timing counter
rs232Tx1Byte ds 1 ;store the byte to be sent in this buffer
rs232Tx2High ds 1 ;High Byte to be transmitted
rs232Tx2Low ds 1 ;Low Byte to be transmitted
rs232Tx2Count ds 1 ;counter to keep track of the bits sent
rs232Tx2Divide ds 1 ;xmit timing counter
rs232Tx2Byte ds 1 ;store the byte to be sent in this buffer
MultiplexBank = $ ;Multipler Bank
isrMultiplex ds 1 ;Used to jump between the ISR Threads when
; an Interrupt occurs
; Bank 2
org bank2_org
bank2 = $
rs232RxBank = $
rs232Rx1Count ds 1 ;counter to keep track of the number of bits received
rs232Rx1Divide ds 1 ;receive timing counter
rs232Rx1Byte ds 1 ;buffer for incoming byte
rs232Byte1 ds 1 ;Used by serial routines
rs232Rx2Count ds 1 ;counter to keep track of the number of bits received
rs232Rx2Divide ds 1 ;receive timing counter
rs232Rx2Byte ds 1 ;buffer for incoming byte
rs232Byte2 ds 1 ;used by serial routines
; Bank 3
org bank3_org
bank3 = $
; Bank 4
org bank4_org
bank4 = $
; Bank 5
org bank5_org
bank5 = $
; Bank 6
org bank6_org
bank6 = $
; Bank 7
org bank7_org
bank7 = $
Port Assignment
RA_latch equ %00000000 ;SX28/48/52 port A latch init ;intial value after reset
RA_DDIR equ %11111111 ;SX28/48/52 port A DDIR value ;0=Output,1=Input
RA_LVL equ %00000000 ;SX28/48/52 port A LVL value ;0=CMOS,1=TTL
RA_PLP equ %00000000 ;SX28/48/52 port A PLP value ;0=Enable,1=Disable
RB_latch equ %10001000 ;SX28/48/52 port B latch init ;intial value after reset
RB_DDIR equ %01110111 ;SX28/48/52 port B DDIR value ;0=Output,1=Input
RB_ST equ %11111111 ;SX28/48/52 port B ST value ;0=Enable,1=Disable
RB_LVL equ %00000000 ;SX28/48/52 port B LVL value ;0=CMOS,1=TTL
RB_PLP equ %11001100 ;SX28/48/52 port B PLP value ;0=Enable,1=Disable
RC_latch equ %00000000 ;SX28/48/52 port C latch init ;intial value after reset
RC_DDIR equ %11111111 ;SX28/48/52 port C DDIR value ;0=Output,1=Input
RC_ST equ %11111111 ;SX28/48/52 port C ST value ;0=Enable,1=Disable
RC_LVL equ %00000000 ;SX28/48/52 port C LVL value ;0=CMOS,1=TTL
RC_PLP equ %00000000 ;SX28/48/52 port C PLP value ;0=Enable,1=Disable
Pin Definitions
rs232Rxpin1 equ rb.6 ;UART1 receive input
rs232Txpin1 equ rb.7 ;UART1 transmit output
rs232Rxpin2 equ rb.2 ;UART2 receive input
rs232Txpin2 equ rb.3 ;UART2 transmit output
Program constants
; UART Constants values
intPeriod = -217
UARTfs = 230400
Num = 4 ; Number of times ISR thread1 is called in the
; ISRMultiplexer
IFDEF U1B1200
UARTBaud1 = 1200
UARTDivide1 = (UARTfs/(UARTBaud1*Num)) ;48
UARTStDelay1 = UARTDivide1 +(UARTDivide1/2)+1
IFDEF U2B9600
UARTBaud2 = 9600
UARTDivide2 = (UARTfs/(UARTBaud2*Num)) ;6
UARTStDelay2 = UARTDivide2 +(UARTDivide2/2)+1
; SX28AC Mode addresses
; *On SX28, all registers addressed via mode are write only, with the exception of
; CMP and WKPND which do an exchange with W.
Exchange addresses
CMP equ $08 ;Exchange Comparator enable/status register with W
WKPND equ $09 ;Exchange MIWU/RB Interrupts pending with W
Port setup (read) addresses
WKED_W equ $0A ;Write MIWU/RB Interrupt edge setup, 1 = falling, 0 = rising
WKEN_W equ $0B ;Write MIWU/RB Interrupt edge setup, 0 = enabled, 1 = disabled
ST_W equ $0C ;Write Port Schmitt Trigger setup, 0 = enabled, 1 = disabled
LVL_W equ $0D ;Write Port Schmitt Trigger setup, 0 = enabled, 1 = disabled
PLP_W equ $0E ;Write Port Schmitt Trigger setup, 0 = enabled, 1 = disabled
DDIR_W equ $0F ;Write Port Direction
ENDIF
Program memory ORG defines
INTERRUPT_ORG equ $0 ; Interrupt must always start at location zero
RESETENTRY_ORG equ $1FB ; The program will jump here on reset
SUBROUTINES_ORG equ $200 ; The subroutines are in this location
STRINGS_ORG equ $300 ; The strings are in the location $300
PAGE3_ORG equ $400 ; Page 3 is empty
MAINPROGRAM_ORG equ $600 ; The main program is in the lastpage of program memory
org INTERRUPT_ORG ; First location in program memory.
; Note 1: The interrupt code must always originate at address $0.
; Interrupt Frequency = (Cycle Frequency / -(retiw value))
; For example: With a retiw value of -217 and an oscillator frequency
; of 50MHz, this code runs every 4.32us.
; Note 2: Mode Register 'M' is not saved in SX 28 but saved in SX 52 when an Interrupt
; occurs. If the code is to run on a SX 28 and 'M' register is used in the ISR,
; then the 'M' register has to be saved at the Start of ISR and restored at the
; End of ISR.
org $0
interrupt ;3
; Interrupt
; Interrupt Frequency = (Cycle Frequency / -(retiw value)) For example:
; With a retiw value of -217 and an oscillator frequency of 50MHz, this code runs
; every 4.32us.
VP:VP Multitasker
; Virtual Peripheral Multitasker : up to 16 individual threads, each running at the
; (interrupt rate/16). Change them below:
;Input variable(s): isrmultiplex: variable used to choose threads
;Output variable(s): None,executes the next thread
;Variable(s) affected: isrmultiplex
;Flag(s) affected: None
;Program Cycles: 9 cycles (turbo mode)
_bank Multiplexbank ;
inc isrMultiplex ; toggle interrupt rate
mov w,isrMultiplex ;
; The code between the tableStart and tableEnd statements MUST be completely within the first
; half of a page. The routines it is jumping to must be in the same page as this table.
tableStart ; Start all tables with this macro
jmp pc+w ;
jmp isrThread1 ;
jmp isrThread2 ;
jmp isrThread3 ;
jmp isrThread4 ;
jmp isrThread1 ;
jmp isrThread5 ;
jmp isrThread6 ;
jmp isrThread7 ;
jmp isrThread1 ;
jmp isrThread8 ;
jmp isrThread9 ;
jmp isrThread10 ;
jmp isrThread1 ;
jmp isrThread11 ;
jmp isrThread12 ;
jmp isrThread13 ;
tableEnd ; End all tables with this macro.
;VP: VP Multitasker
; ISR TASKS
isrThread1 ; Serviced at ISR rate/4
; Virtual Peripheral: Universal Asynchronous Receiver Transmitter (UART) These routines send
; and receive RS232 serial data, and are currently configured (though modifications can be
; made) for the popular "No parity-checking, 8 data bit, 1 stop bit" (N,8,1) data format.
; The VP below has 2 UARTS implemented - UART1 & UART2. Both the UARTs can work at independent
; Baud Rates.
; RECEIVING: The rs232Rx1flag & rs232Rx2flag are set high whenever a valid byte of data has
; been received and it is the calling routine's responsibility to reset this flag once the
; incoming data has been collected.
; TRANSMITTING: The transmit routine requires the data to be inverted and loaded
; (rs232Txhigh+rs232Txlow) register pair (with the inverted 8 data bits stored in
; rs232Txhigh and rs232Txlow bit 7 set high to act as a start bit). Then the number of bits
; ready for transmission (10=1 start + 8 data + 1 stop) must be loaded into the rs232Txcount
; register. As soon as this latter is done, the transmit routine immediately begins sending
; the data. This routine has a varying execution rate and therefore should always be
; placed after any timing-critical virtual peripherals such as timers,
; adcs, pwms, etc.
; Note: The transmit and receive routines are independent and either may be removed for each
; of the UARTs. The initial "_bank rs232TxBank" & "_bank rs232RxBank" (common)
; instruction is kept for Transmit & Receive routines.
; Input variable(s) : rs232Tx1Low (only high bit used), rs232Tx1High, rs232Tx1Count
; If rs232Tx1Flag SET, then transmit on UART1
; rs232Tx2Low (only high bit used), rs232Tx2High, rs232Tx2Count
; If rs232Tx2Flag SET, then transmit on UART2
; Output variable(s) : rs232Rx1Flag, rs232Rx1Byte
; rs232Rx2Flag, rs232Rx2Byte
; Variable(s) affected : rs232Tx1Divide, rs232Rx1Divide, rs232Rx1Count
; rs232Tx2Divide, rs232Rx2Divide, rs232Rx2Count
; Flag(s) affected : rs232Tx1Flag, rs232Tx2Flag
; rs232Rx1Flag, rs232Rx1Flag
; Program cycles: 22 worst case for Tx, 23 worst case for Rx
; Variable Length? Yes.
UART1
rs232Transmit
_bank rs232TxBank ;2 switch to serial register bank
sb rs232Tx1FLag ;1
jmp rs232Receive1 ;1
decsz rs232Tx1Divide ;1 only execute the transmit routine
mov w,#UARTDivide1 ;1 load UART1 baud rate (50MHz)
mov rs232Tx1Divide,w ;1
test rs232Tx1Count ;1 are we sending?
snz ;1
:txbit clc ;1 yes, ready stop bit
rr rs232Tx1High ;1 and shift to next bit
rr rs232Tx1Low ;1
dec rs232Tx1Count ;1 decrement bit counter
snb rs232Tx1Low.6 ;1 output next bit
clrb rs232TxPin1 ;1
sb rs232Tx1Low.6 ;1
setb rs232TxPin1 ;1
snz ;1
clrb rs232Tx1Flag ;1,22
rs232Receive1
_bank rs232RxBank ;2
sb rs232RxPin1 ;1 get current rx bit
clc ;1
snb rs232RxPin1 ;1
stc ;1
test rs232Rx1Count ;1 currently receiving byte?
sz ;1
jmp :rxbit ;1 if so, jump ahead
mov w,#9 ;1 in case start, ready 9 bits
mov rs232Rx1Count,w ;1 it is, so renew bit count
mov w,#UARTStDelay1 ;1 ready 1.5 bit periods (50MHz)
mov rs232Rx1Divide,w ;1
:rxbit decsz rs232Rx1Divide ;1 middle of next bit?
jmp :rs232RxOut1 ;1
mov w,#UARTDivide1 ;1 yes, ready 1 bit period (50MHz)
dec rs232Rx1Count ;1 last bit?
sz ;1 if not
rr rs232Rx1Byte ;1 then save bit
snz ;1 if so,
setb rs232Rx1Flag ;1,23 then set flag
:rs232RxOut1
UART2
sb rs232Tx2flag ;1
jmp rs232Receive2 ;1
decsz rs232Tx2Divide ;1 only execute the transmit routine
mov w,#UARTDivide2 ;1 load UART2 baud rate (50MHz)
mov rs232Tx2Divide,w ;1
test rs232Tx2Count ;1 are we sending?
snz ;1
:txbit stc ;1 yes, ready stop bit
rr rs232Tx2High ;1 and shift to next bit
rr rs232Tx2Low ;1
dec rs232Tx2Count ;1 decrement bit counter
snb rs232Tx2Low.6 ;1 output next bit
clrb rs232TxPin2 ;1
sb rs232Tx2Low.6 ;1
setb rs232TxPin2 ;1
snz ;1
clrb rs232Tx2Flag ;1,22
rs232Receive2
sb rs232RxPin2 ;1 get current rx bit
clc ;1
snb rs232RxPin2 ;1
stc ;1
test rs232Rx2Count ;1 currently receiving byte?
sz ;1
sc ;1 skip ahead if not start bit
mov rs232Rx2Count,w ;1 it is, so renew bit count
mov w,#UARTStDelay2 ;1 ready 1.5 bit periods (50MHz)
mov rs232Rx2Divide,w ;1
:rxbit decsz rs232Rx2Divide ;1 middle of next bit?
jmp :rs232RxOut2 ;1
mov w,#UARTDivide2 ;1 yes, ready 1 bit period (50MHz)
dec rs232Rx2Count ;1 last bit?
sz ;1 if not
rr rs232Rx2Byte ;1 then save bit
snz ;1 if so,
setb rs232Rx2Flag ;1,23 then set flag
:rs232RxOut2
UARTOut
;===================================== PUT YOUR OWN VPs HERE==================================
; Input variable(s):
; Output variable(s):
; Variable(s) affected:
; Flag(s) affected:
jmp isrOut ; 7 cycles until mainline program resumes execution
isrThread2 ; Serviced at ISR rate/16
isrThread3 ; Serviced at ISR rate/16
isrThread4 ; Serviced at ISR rate/16
isrThread5 ; Serviced at ISR rate/16
isrThread6 ; Serviced at ISR rate/16
isrThread7 ; Serviced at ISR rate/16
isrThread8 ; Serviced at ISR rate/16
isrThread9 ; Serviced at ISR rate/16
isrThread10 ; Serviced at ISR rate/16
isrThread11 ; Serviced at ISR rate/16
isrThread12 ; Serviced at ISR rate/16
isrThread13 ; Serviced at ISR rate/16
; This thread must reload the isrMultiplex register
_bank Multiplexbank
mov isrMultiplex,#255 ;reload isrMultiplex so isrThread1 will be run on the
; next interrupt.
; since it is the last one to run in a rotation.
isrOut
; Set Interrupt Rate
isr_end
mov w,#intPeriod ;refresh RTCC on return
;(RTCC = 217, no. of instructions executed in the ISR)
retiw ;return from the interrupt
; End of the Interrupt Service Routine
; RESET VECTOR
Reset Entry
org RESETENTRY_ORG
resetEntry ; Program starts here on power-up
page _resetEntry
jmp _resetEntry
UART Subroutines
org SUBROUTINES_ORG
; Function : getbyte
; INPUTS : rs232RX1Flag,rs232Rx2Flag
; OUTPUTS : Received byte in rs232Rx1Byte or rs232Rx2Byte
; Get byte via serial port and echo it back to the serial port
getbyte
getbyte1
_bank rs232RxBank ; switch to rs232 bank
sb rs232RX1Flag ; check if byte has been received by UART1
jmp getbyte2
clrb rs232Rx1Flag ; reset the receive flag
mov w,rs232Rx1Byte ; store byte (copy using W)
mov rs232Byte1,w
getbyte2 sb rs232Rx2Flag ; check if byte has been received by UART2
jmp [noparse]:o[/noparse]ut
clrb rs232Rx2Flag
mov w,rs232Rx2Byte
mov rs232Byte2,w
[noparse]:o[/noparse]ut retp
; Function : sendbyte
; INPUTS : rs232Tx1Flag set, rs232Tx1Byte - the byte to be sent via UART1
; rs232Tx2Flag set, rs232Tx2Byte- the byte to be sent via UART2
; OUTPUTS : Outputs The byte via RS-232 UART1/UART2
; Send byte via serial port
; Note: Before calling a sendbyte in Main, it should be ensured that respective
; flag of the UART rs232Tx1Flag/rs232Tx2Flag is CLEAR, and if clear then a
; byte can be sent, then the respective UART flag must be SET.
sendbyte
sendbyte1
_bank rs232TxBank
test rs232Tx1Count
sz
jmp sendbyte2
sb rs232Tx1Flag
jmp sendbyte2
mov w,rs232Tx1Byte
not w ; ready bits (inverse logic)
mov rs232Tx1High,w ; store data byte
setb rs232Tx1Low.7 ; set up start bit
mov w,#10 ; 1 start + 8 data + 1 stop bit
mov rs232Tx1Count,w
sendbyte2 test rs232Tx2Count
sz
jmp sendbyte1
sb rs232Tx2Flag
mov w,rs232Tx2Byte
; not w
mov rs232Tx2High,w ; store data byte
clrb rs232Tx2Low.7 ; set up start bit
mov rs232Tx2Count,w
[noparse]:o[/noparse]ut retp ; leave and fix page bits
; Function : sendstring1
; Care should be taken that the srings are located within program
; memory locations $300-$3ff as the area
; INPUTS : 'w', The address of a null-terminated string in program memory
; OUTPUTS : outputs the string via RS-232 UART1
; Send string pointed to by address in W register
; Note: This routine is a locking routine in the sense that the function returns
; to 'main' (the calling function) only after all the bytes of the string
; are transmitted (until 00H is encountered).
sendstring1 _bank rs232TxBank
mov localTemp1,w ; store string address
:string test rs232Tx1Count
sz
jmp :string
setb rs232Tx1Flag ; SET flag for UART1
mov w,#STRINGS_ORG>>8 ; with indirect addressing
mov m,w
mov w,localTemp1 ; read next string character
iread ; using the mode register
test w ; are we at the last char?
snz ; if not=0, skip ahead
jmp [noparse]:o[/noparse]ut ; yes, leave & fix page bits
_bank rs232TxBank
mov rs232Tx1Byte,w
call sendByte1 ; not 0, so send character
_bank rs232TxBank
inc localTemp1 ; point to next character
jmp :string ; loop until done
[noparse]:o[/noparse]ut clrb rs232Tx1Flag
mov w,#$1F ; reset the mode register
mov m,w
retp
; Function : sendstring2
; OUTPUTS : outputs the string via RS-232 UART2
sendstring2 _bank rs232TxBank
:string test rs232Tx2Count
sz
jmp :string
setb rs232Tx2Flag ; SET flag for UART2
mov m,w
_bank rs232TxBank
mov rs232Tx2Byte,w
call sendByte2 ; not 0, so send character
_bank rs232TxBank
[noparse]:o[/noparse]ut clrb rs232Tx2Flag
mov m,w
retp
org STRINGS_ORG ; This label defines where strings are kept in program space.
String Data
;VP: RS232 Transmit
_welcome dw 84,147,131,145,195,136,140,255,0
_zero dw 167, 7, 128, 7, 149, 164, 0
_one dw 147, 14, 136, 8, 141, 0
_two dw 8, 191, 162, 0
_three dw 8, 190, 148, 8, 128, 0
_four dw 186, 7, 137, 153, 0
_five dw 186, 157, 166, 0
_six dw 8, 187, 129, 14, 194, 7, 187, 0
_seven dw 8, 187, 7, 131, 166, 131, 141, 0
_eight dw 154, 4, 191, 0
_nine dw 141, 14, 157, 141, 0
_point dw 7, 199, 7, 156, 15, 141, 15, 191, 0
_desee dw 8, 174, 128, 128, 5, 6, 8, 187, 128, 128, 0
_asee dw 8, 154, 1, 6, 8, 187, 26, 2, 128, 128, 0
_volts dw 166, 26, 1, 164, 26, 1, 146, 193, 0
_amps dw 133, 133, 140, 140, 199, 199, 8, 193, 0
_temper dw 191, 7, 131, 140, 7, 0, 198, 7, 148, 7, 134, 8, 191, 139, 148,0
_milli dw 140, 129, 145, 145, 128, 128, 0
_micro dw 140, 140, 157, 196, 196, 7, 148, 136, 8, 137, 0
_kilo dw 194, 7, 128, 14, 146, 137, 0
_mega dw 22, 88, 23, 5,0
_nano dw 14, 141, 7, 131, 0, 141, 141, 164,0
_hertz dw 183, 14, 148, 191, 193, 0
_negative dw 141, 130, 178, 133, 191, 129, 166, 0
_henries dw 184, 131, 131, 141, 141, 148, 148, 128, 15, 193, 0
_celcius dw 187, 130, 145, 187, 7, 128, 7, 134, 187, 0
_farad dw 186, 186, 132, 132, 14, 148, 132, 132, 15, 175, 187, 0
_ohms dw 164, 140, 15, 193
_cap dw 7, 195, 132, 132, 0, 199, 0, 132, 187, 129, 191, 132, 141, 187, 0
org PAGE3_ORG
jmp $
Main Program
; Program execution begins here on power-up or after a reset
org MAINPROGRAM_ORG
_resetEntry
Initialise all port configuration
_mode ST_W ;point MODE to write ST register
mov w,#RB_ST ;Setup RB Schmitt Trigger, 0 = enabled, 1 = disabled
mov !rb,w
mov w,#RC_ST ;Setup RC Schmitt Trigger, 0 = enabled, 1 = disabled
mov !rc,w
_mode LVL_W ;point MODE to write LVL register
mov w,#RA_LVL ;Setup RA CMOS or TTL levels, 1 = TTL, 0 = CMOS
mov !ra,w
mov w,#RB_LVL ;Setup RB CMOS or TTL levels, 1 = TTL, 0 = CMOS
mov !rb,w
mov w,#RC_LVL ;Setup RC CMOS or TTL levels, 1 = TTL, 0 = CMOS
mov !rc,w
_mode PLP_W ;point MODE to write PLP register
mov w,#RA_PLP ;Setup RA Weak Pull-up, 0 = enabled, 1 = disabled
mov !ra,w
mov w,#RB_PLP ;Setup RB Weak Pull-up, 0 = enabled, 1 = disabled
mov !rb,w
mov w,#RC_PLP ;Setup RC Weak Pull-up, 0 = enabled, 1 = disabled
mov !rc,w
_mode DDIR_W ;point MODE to write DDIR register
mov w,#RA_DDIR ;Setup RA Direction register, 0 = output, 1 = input
mov !ra,w
mov w,#RB_DDIR ;Setup RB Direction register, 0 = output, 1 = input
mov !rb,w
mov w,#RC_DDIR ;Setup RC Direction register, 0 = output, 1 = input
mov !rc,w
mov w,#RA_latch ;Initialize RA data latch
mov ra,w
mov w,#RB_latch ;Initialize RB data latch
mov rb,w
mov w,#RC_latch ;Initialize RC data latch
mov rc,w
Clear all Data RAM locations
;SX18/20/28 RAM clear routine
clr fsr ;reset all ram banks
:zeroRam sb fsr.4 ;are we on low half of bank?
setb fsr.3 ; To clear from 08 - Global Registers
clr ind ;clear using indirect addressing
incsz fsr ;repeat until done
jmp :zeroRam
; Initialize program/VP registers
_bank rs232TxBank ;select rs232 bank
mov w,#UARTDivide1 ;load rs232Tx1Divide with UART1 baud rate
mov w,#UARTDivide2 ;load rs232Tx1Divide with UART2 baud rate
mov rs232Tx2Divide,w ;I changed to rs232Tx2Divide
; Setup and enable RTCC interrupt, WREG register, RTCC/WDT prescaler
RTCC_ON = %10000000 ;Enables RTCC at address $01 (RTW hi)
;*WREG at address $01 (RTW lo) by default
RTCC_ID = %01000000 ;Disables RTCC edge interrupt (RTE_IE hi)
;*RTCC edge interrupt (RTE_IE lo) enabled by default
RTCC_INC_EXT = %00100000 ;Sets RTCC increment on RTCC pin transition (RTS hi)
;*RTCC increment on internal instruction (RTS lo) is default
RTCC_FE = %00010000 ;Sets RTCC to increment on falling edge (RTE_ES hi)
;*RTCC to increment on rising edge (RTE_ES lo) is default
RTCC_PS_ON = %00000000 ;Assigns prescaler to RTCC (PSA lo)
RTCC_PS_OFF = %00001000 ;Assigns prescaler to WDT (PSA hi)
PS_000 = %00000000 ;RTCC = 1:2, WDT = 1:1
PS_001 = %00000001 ;RTCC = 1:4, WDT = 1:2
PS_010 = %00000010 ;RTCC = 1:8, WDT = 1:4
PS_011 = %00000011 ;RTCC = 1:16, WDT = 1:8
PS_100 = %00000100 ;RTCC = 1:32, WDT = 1:16
PS_101 = %00000101 ;RTCC = 1:64, WDT = 1:32
PS_110 = %00000110 ;RTCC = 1:128, WDT = 1:64
PS_111 = %00000111 ;RTCC = 1:256, WDT = 1:128
OPTIONSETUP equ RTCC_PS_OFF|PS_111 ; the default option setup for this program.
mov w,#OPTIONSETUP ; setup option register for RTCC interrupts enabled
mov !option,w ; and prescaler assigned to WDT.
jmp @mainLoop
MAIN PROGRAM CODE
mainLoop
mov w, #_welcome
setb rs232Tx1Flag
call @sendstring2
jmp mainloop1
mainloop1
jmp mainloop1
END ;End of program code
It also appears that a little too much code has been trimmed down in the UART's. UART 1 is missing a "sc" instruction for the receiver to properly wait for the start bit before it starts sampling the bits for the next byte.
If I were you, I would simplify this code down to one UART (just comment out the second one), and remove all of the multiplexing code that you don't even appear to be using. Later, you can slowly add in more complexity.