Well, I'm looking to control a large boiler. Basically I want a
temperature reading circuit and the based on the temperature, switch
a 240V 20AMP element on. I'm new to electronics, but I understand
how the basic stamp works ie. I do some programming. any suggestions?

Comments

  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 15:51
    jjlwork,

    What you want to do is easy, and a BS1 would be more than capable for the
    job. With an LM34, you can easily make an in-line water temp. sensor, and
    use the RCTIME command to determine the temperature. A relay would be used
    to switch the 240V element on and off.

    Jonathan

    www.madlabs.info

    Original Message
    From: "jjlwork" <jjlwork@y...>
    To: <basicstamps@yahoogroups.com>
    Sent: Thursday, August 28, 2003 11:00 PM
    Subject: [noparse][[/noparse]basicstamps] New guy looking for a quick fix


    > Well, I'm looking to control a large boiler. Basically I want a
    > temperature reading circuit and the based on the temperature, switch
    > a 240V 20AMP element on. I'm new to electronics, but I understand
    > how the basic stamp works ie. I do some programming. any suggestions?
    >
    >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the Subject and
    Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
    >
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 16:28
    Hmm.. this sounds a little scary. A mistake in code that keeps the
    boiler on too long, that leads to too much pressure, that leads to...
    umm.. bang.

    [noparse]:([/noparse]

    The concept and implementation of this type of circuit is pretty straight
    forward and a stamp circuit is well suited. Frankly, I'd *much* rather
    have the stamp watching a possibly dangerous process than have a Windows
    box with some code doing the same thing (could lead to a new definition
    of MSBlaster!!) [noparse];)[/noparse]

    However, I would want to make DANG sure the code was working properly
    before I used it on a boiler that could do *real* damage if it became
    over-pressured. Maybe a fail-safe implementation i.e. any anomalous state
    leads to boiler power OFF. Just my $0.02. [noparse]:)[/noparse]

    Vern

    --
    Vern Graner CNE/CNA/SSE | "If the network is down, then you're
    Senior Systems Engineer | obviously incompetent so why are we
    Texas Information Services | paying you? Of course, if the network
    vern@t... www.txis.com | is up, then we obviously don't need
    Cell 507-7851 Desk 328-8947 | you, so why are we paying you?" VLG



    jjlwork said:
    > Well, I'm looking to control a large boiler. Basically I want a
    > temperature reading circuit and the based on the temperature, switch
    > a 240V 20AMP element on. I'm new to electronics, but I understand
    > how the basic stamp works ie. I do some programming. any suggestions?
    >
    >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the Subject and
    > Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
    >
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 16:56
    Vernon,

    You bet. I would keep the original overheat shut off and overflow valves in
    place for sure.

    Jonathan

    www.madlabs.info

    Original Message
    From: "Vernon Graner" <vern@t...>
    To: <basicstamps@yahoogroups.com>
    Sent: Friday, August 29, 2003 8:28 AM
    Subject: Re: [noparse][[/noparse]basicstamps] New guy looking for a quick fix


    > Hmm.. this sounds a little scary. A mistake in code that keeps the
    > boiler on too long, that leads to too much pressure, that leads to...
    > umm.. bang.
    >
    > [noparse]:([/noparse]
    >
    > The concept and implementation of this type of circuit is pretty straight
    > forward and a stamp circuit is well suited. Frankly, I'd *much* rather
    > have the stamp watching a possibly dangerous process than have a Windows
    > box with some code doing the same thing (could lead to a new definition
    > of MSBlaster!!) [noparse];)[/noparse]
    >
    > However, I would want to make DANG sure the code was working properly
    > before I used it on a boiler that could do *real* damage if it became
    > over-pressured. Maybe a fail-safe implementation i.e. any anomalous state
    > leads to boiler power OFF. Just my $0.02. [noparse]:)[/noparse]
    >
    > Vern
    >
    > --
    > Vern Graner CNE/CNA/SSE | "If the network is down, then you're
    > Senior Systems Engineer | obviously incompetent so why are we
    > Texas Information Services | paying you? Of course, if the network
    > vern@t... www.txis.com | is up, then we obviously don't need
    > Cell 507-7851 Desk 328-8947 | you, so why are we paying you?" VLG
    >
    >
    >
    > jjlwork said:
    > > Well, I'm looking to control a large boiler. Basically I want a
    > > temperature reading circuit and the based on the temperature, switch
    > > a 240V 20AMP element on. I'm new to electronics, but I understand
    > > how the basic stamp works ie. I do some programming. any suggestions?
    > >
    > >
    > >
    > > To UNSUBSCRIBE, just send mail to:
    > > basicstamps-unsubscribe@yahoogroups.com
    > > from the same email address that you subscribed. Text in the Subject
    and
    > > Body of the message will be ignored.
    > >
    > >
    > > Your use of Yahoo! Groups is subject to
    http://docs.yahoo.com/info/terms/
    > >
    > >
    > >
    >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the Subject and
    Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
    >
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 17:24
    Well, while I wholeheartedly agree with the cautionary statement, its not
    quite as dangerous as you might think.

    Although electronics are in control of general operation, all boilers have
    (by law) safety controls that keep things from blowing up. Typically,
    automatic controls will cycle between two different temperature - high and
    low operating setpoints. These can be virtually anything, from a Stamp to an
    Aquastat. I've worked on Babcox and Wilcox ship-borne boilers (Destroyers -
    550PSI Superheat), Vapour Clarkson auxiliary boilers (100psi saturated
    steam), Fire tube and water tube LP boilers and hot water boilers (just big
    versions of your home gas fired hot water heater). They all share common
    safety devices.

    1) High temperature limit controller - If the high operating setpoint is
    surpassed, this shuts it down.
    2) Low water sensor - run low on water and this shuts it down before you
    start burning tubes

    These two controls will override the operating controls.

    3) Pressure relief valve - Vents excess pressure. This isn't typically
    connected to the control system at all and will not shut down the boiler.

    An awful lot of things have to fail in order for real damage to occur.




    >
    Original Message
    > From: Vernon Graner [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=Rb0aEettFAzYjSM7fvfuiyQRsrFQo_Ku50jTZ64J8MBDYUKCm9cACuIMaPh44Q0OcfuVs7c]vern@t...[/url
    > Sent: August 29, 2003 8:28 AM
    > To: basicstamps@yahoogroups.com
    > Subject: Re: [noparse][[/noparse]basicstamps] New guy looking for a quick fix
    >
    >
    > Hmm.. this sounds a little scary. A mistake in code that keeps the
    > boiler on too long, that leads to too much pressure, that leads to...
    > umm.. bang.
    >
    > [noparse]:([/noparse]
    >
    > The concept and implementation of this type of circuit is pretty straight
    > forward and a stamp circuit is well suited. Frankly, I'd *much* rather
    > have the stamp watching a possibly dangerous process than have a Windows
    > box with some code doing the same thing (could lead to a new definition
    > of MSBlaster!!) [noparse];)[/noparse]
    >
    > However, I would want to make DANG sure the code was working properly
    > before I used it on a boiler that could do *real* damage if it became
    > over-pressured. Maybe a fail-safe implementation i.e. any anomalous state
    > leads to boiler power OFF. Just my $0.02. [noparse]:)[/noparse]
    >
    > Vern
    >
    > --
    > Vern Graner CNE/CNA/SSE | "If the network is down, then you're
    > Senior Systems Engineer | obviously incompetent so why are we
    > Texas Information Services | paying you? Of course, if the network
    > vern@t... www.txis.com | is up, then we obviously don't need
    > Cell 507-7851 Desk 328-8947 | you, so why are we paying you?" VLG
    >
    >
    >
    > jjlwork said:
    > > Well, I'm looking to control a large boiler. Basically I want a
    > > temperature reading circuit and the based on the temperature, switch
    > > a 240V 20AMP element on. I'm new to electronics, but I understand
    > > how the basic stamp works ie. I do some programming. any suggestions?
    > >
    > >
    > >
    > > To UNSUBSCRIBE, just send mail to:
    > > basicstamps-unsubscribe@yahoogroups.com
    > > from the same email address that you subscribed. Text in the
    > Subject and
    > > Body of the message will be ignored.
    > >
    > >
    > > Your use of Yahoo! Groups is subject to
    > http://docs.yahoo.com/info/terms/
    > >
    > >
    > >
    >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the
    > Subject and Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
    >
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 17:42
    Use a temperature controller rated for boiler control. Boilers are not to
    be played with; it would be a shame to have an explosion because of a
    programming or hardware failure.

    jim
    http://www.geocities.com/jimforkin2003/


    Original Message
    From: jjlwork [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=X2W345q5GPUOHWYxKsZ-Y9UrxzVeW3GnLjzT755XTCewHm8v6HC57O8rnjcZ4nZNMfk_kZlr]jjlwork@y...[/url
    Sent: Friday, August 29, 2003 2:01 AM
    To: basicstamps@yahoogroups.com
    Subject: [noparse][[/noparse]basicstamps] New guy looking for a quick fix


    Well, I'm looking to control a large boiler. Basically I want a
    temperature reading circuit and the based on the temperature, switch
    a 240V 20AMP element on. I'm new to electronics, but I understand
    how the basic stamp works ie. I do some programming. any suggestions?



    To UNSUBSCRIBE, just send mail to:
    basicstamps-unsubscribe@yahoogroups.com
    from the same email address that you subscribed. Text in the Subject and
    Body of the message will be ignored.


    Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 18:00
    --- In basicstamps@yahoogroups.com, PatM <pmeloy@s...> wrote:
    > Well, while I wholeheartedly agree with the cautionary statement,
    its not
    > quite as dangerous as you might think.
    >
    > Although electronics are in control of general operation, all
    boilers have
    > (by law) safety controls that keep things from blowing up.
    Typically,
    > automatic controls will cycle between two different temperature -
    high and
    > low operating setpoints. These can be virtually anything, from a
    Stamp to an
    > Aquastat. I've worked on Babcox and Wilcox ship-borne boilers
    (Destroyers -
    > 550PSI Superheat), Vapour Clarkson auxiliary boilers (100psi
    saturated
    > steam), Fire tube and water tube LP boilers and hot water boilers
    (just big
    > versions of your home gas fired hot water heater). They all share
    common
    > safety devices.
    >
    > 1) High temperature limit controller - If the high operating
    setpoint is
    > surpassed, this shuts it down.
    > 2) Low water sensor - run low on water and this shuts it down
    before you
    > start burning tubes
    >
    > These two controls will override the operating controls.
    >
    > 3) Pressure relief valve - Vents excess pressure. This isn't
    typically
    > connected to the control system at all and will not shut down the
    boiler.
    >
    > An awful lot of things have to fail in order for real damage to
    occur.


    You are correct, but about 99.9% of the stuff we do will self
    destruct in a neat flash of light or puff of smoke.

    boilers have all those safety controls from all the people who died
    after a failure.

    Enhancing a control of a boiler might offer energy savings, but in NJ
    abnd PA, you must be liscensed to operate a boiler, and a liscensed
    person must be on-site when the boiler is operating.

    In my 25 years in HVAC, I have only heard of one boiler accident and
    only one death.

    My recomendation is to double check your controls and make sure they
    do not superceed or override any other controls.

    proceed, but with caution.

    as far as sensors, use sensors approved for the application, they may
    cost more, but the temperatures and pressuers involved will have been
    proven on those devices.

    Dave
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 18:23
    Just a quick take on boiler safety...Our local fair.


    http://www.savannahnow.com/stories/073101/LOCexplosap.shtml
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 18:33
    jjlwork said:
    >I personally do not think there is any
    > chance of explosion! [noparse][[/noparse]snip] I'm making BEER!

    Heh! Maybe just an explosaion in people willing to come and "help" with
    your projects! [noparse]:D[/noparse]

    "hmmm Lemme taste that.. nah I think we need to add a PAUSE 500 command
    and retaste--- er... reTEST!" [noparse]:)[/noparse]

    Vern

    --
    Vern Graner CNE/CNA/SSE | "If the network is down, then you're
    Senior Systems Engineer | obviously incompetent so why are we
    Texas Information Services | paying you? Of course, if the network
    vern@t... www.txis.com | is up, then we obviously don't need
    Cell 507-7851 Desk 328-8947 | you, so why are we paying you?" VLG
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 18:36
    A lot of you have provided some good information, some of you
    expressed safety concerns, I personally do not think there is any
    chance of explosion! Maybe I should elaborate more. I'm making BEER!
    Basically I have to mash(steep) grains in water between 150F - 158F.
    I'm using a modified 10 Gal stainless steel pot with a heating
    element in it. I want to monitor the temperature of the mash and any
    time it drops below 145F turn the element on or goes over 150 turn
    the element off. I want to take it one step further as well, after
    the grain has been steeping for an hour I want to turn a pump on and
    open some sort of electric valve to transfer the liquid through a
    filter to another pot with the same type of setup for boiling. I
    want an alarm to sound at three diferent time intervals...these are
    the intervals that I add hops to the boil add flavour. This is a
    little more complicated than this but the rest are details.
    Basically it would look something like this:

    Process:

    1) Heat water to 158F
    2) when water reaches 158F start timer and hold temp between 150- 158
    Start stiring arm moptor.
    3) After 1 hour open drain valve and start pump
    4)check to see if tank is empty every second if it is shut of the
    pump and start element #2
    5) bring water to boil(temp TBD) and start timer
    6) at 3 diferent (TBD) intervals sound alarm for adding hops
    7) After 1 hour start pump#2 and open Drain#2 to fill fermentor(Same
    as before)
    8) Stop

    maybe I could put another process so that if a maximum mash
    temperature or boiling temperature is reached then an alrm will
    sound.
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 18:43
    Ahhhh!!!! This is what defines the fine line between...

    "people who make beer" and "people who drink beer"

    ...and then there are those who "drink and make beer"

    I wonder what the threshold level is before too much drinking
    causes the beer not to be made - grin

    Can we set this test up with a Stamp?


    -Beau Schwabe (why not it's Friday!! - I love to program Drunk!!)


    >jjlwork said:
    > >I personally do not think there is any
    > > chance of explosion! [noparse][[/noparse]snip] I'm making BEER!
    >
    >Heh! Maybe just an explosaion in people willing to come and "help" with
    >your projects! [noparse]:D[/noparse]
    >
    >"hmmm Lemme taste that.. nah I think we need to add a PAUSE 500 command
    >and retaste--- er... reTEST!" [noparse]:)[/noparse]
    >
    >Vern
    >
    >--
    >Vern Graner CNE/CNA/SSE | "If the network is down, then you're
    >Senior Systems Engineer | obviously incompetent so why are we
    >Texas Information Services | paying you? Of course, if the network
    >vern@t... www.txis.com | is up, then we obviously don't need
    >Cell 507-7851 Desk 328-8947 | you, so why are we paying you?" VLG
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 18:55
    >
    Original Message
    > From: Dave Mucha [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=LPVfQKP3qzc9CNunYvsl2Wkq8mf4oG684GiWzpj9UiryZJj7Xg1hvcVLyAVKePvradBWguBJT3Sx]davemucha@j...[/url
    > Sent: August 29, 2003 10:01 AM
    > To: basicstamps@yahoogroups.com
    > Subject: [noparse][[/noparse]basicstamps] Re: New guy looking for a quick fix
    >
    > boilers have all those safety controls from all the people who died
    > after a failure.

    Which is where most regulation originate - sad to say.

    > Enhancing a control of a boiler might offer energy savings, but in NJ
    > abnd PA, you must be liscensed to operate a boiler, and a liscensed
    > person must be on-site when the boiler is operating.

    Yep, I'm one of them - basically every jurisdiction has similar rules.
    Though the coverage required is determined by heating surface and/or
    pressure of the unit. Here in British columbia they have to be fairly large
    to require an operator on site. In the 11 recreation centres we have, not
    one of the boilers requires an operator. Doing actual work on them usually
    requires a gas ticket and/or electrical ticket depending on what you're
    doing. If you alter them in any way you automatically terminate your licence
    to operate the unit and must have an inspector re-evaluate the unit before
    operating it again. Usually you'd contact the inspector and discuss the
    alteration long before doing anything - to get their go-ahead.


    Haven't seen a boiler accident yet. Been at it 23 years myself.
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 19:07
    I would just like to add that this is not a pressurized sytem, there
    are no air tight lids, the potential for accident id if I get a boil
    over...could be an electrifying experience! However I can implemnt
    some safety circuits.

    --- In basicstamps@yahoogroups.com, PatM <pmeloy@s...> wrote:
    >
    > >
    Original Message
    > > From: Dave Mucha [noparse][[/noparse]mailto:davemucha@j...]
    > > Sent: August 29, 2003 10:01 AM
    > > To: basicstamps@yahoogroups.com
    > > Subject: [noparse][[/noparse]basicstamps] Re: New guy looking for a quick fix
    > >
    > > boilers have all those safety controls from all the people who
    died
    > > after a failure.
    >
    > Which is where most regulation originate - sad to say.
    >
    > > Enhancing a control of a boiler might offer energy savings, but
    in NJ
    > > abnd PA, you must be liscensed to operate a boiler, and a
    liscensed
    > > person must be on-site when the boiler is operating.
    >
    > Yep, I'm one of them - basically every jurisdiction has
    similar rules.
    > Though the coverage required is determined by heating surface
    and/or
    > pressure of the unit. Here in British columbia they have to be
    fairly large
    > to require an operator on site. In the 11 recreation centres we
    have, not
    > one of the boilers requires an operator. Doing actual work on them
    usually
    > requires a gas ticket and/or electrical ticket depending on what
    you're
    > doing. If you alter them in any way you automatically terminate
    your licence
    > to operate the unit and must have an inspector re-evaluate the
    unit before
    > operating it again. Usually you'd contact the inspector and
    discuss the
    > alteration long before doing anything - to get their go-ahead.
    >
    >
    > Haven't seen a boiler accident yet. Been at it 23 years myself.
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 19:32
    jj,

    Aha, you are making a beer machine! I myself have made a RIMS, but it was
    before I used Stamps, so it has a PID controller. It is a 10 gallon,
    auto-sparging and has a built in counter flow chiller. A pump circulates the
    wort and heats it as it passes by an electric element. This also uses the
    grain bed as a filter, so my beer is super clear. The mash tun is a Sanky
    keg with the top cut open. It has 2 inches of insulation, and is covered
    with sheet metal. It isn't exactly what I would make if I was to do it
    again, but it works really well.

    Contact me off-list if you want, there are lots of issues, like: Is it worth
    it to have a stirrer? I get great extraction without one, and it makes for
    other issues. For example, it makes it harder to insulate the top, and it
    disturbs the grain bed. This means longer circulation times to get decent
    clarity, and if you are doing that by hand, ugh. If you are using a false
    bottom, it can make a "stuck" mash. Also, with an electric element in direct
    contact with the wort, carmalization occurs, which results in color change
    and the production of un-fermentables. So the less you have to run the
    heater the better, unless you are making dark beers, in which case it can be
    good. With proper insulation very little heating is required.

    What size batches are you making? What is the mash tun to be made of?

    Jonathan

    www.madlabs.info

    Original Message
    From: "jjlwork" <jjlwork@y...>
    To: <basicstamps@yahoogroups.com>
    Sent: Friday, August 29, 2003 10:36 AM
    Subject: [noparse][[/noparse]basicstamps] New guy looking for a quick fix


    > A lot of you have provided some good information, some of you
    > expressed safety concerns, I personally do not think there is any
    > chance of explosion! Maybe I should elaborate more. I'm making BEER!
    > Basically I have to mash(steep) grains in water between 150F - 158F.
    > I'm using a modified 10 Gal stainless steel pot with a heating
    > element in it. I want to monitor the temperature of the mash and any
    > time it drops below 145F turn the element on or goes over 150 turn
    > the element off. I want to take it one step further as well, after
    > the grain has been steeping for an hour I want to turn a pump on and
    > open some sort of electric valve to transfer the liquid through a
    > filter to another pot with the same type of setup for boiling. I
    > want an alarm to sound at three diferent time intervals...these are
    > the intervals that I add hops to the boil add flavour. This is a
    > little more complicated than this but the rest are details.
    > Basically it would look something like this:
    >
    > Process:
    >
    > 1) Heat water to 158F
    > 2) when water reaches 158F start timer and hold temp between 150- 158
    > Start stiring arm moptor.
    > 3) After 1 hour open drain valve and start pump
    > 4)check to see if tank is empty every second if it is shut of the
    > pump and start element #2
    > 5) bring water to boil(temp TBD) and start timer
    > 6) at 3 diferent (TBD) intervals sound alarm for adding hops
    > 7) After 1 hour start pump#2 and open Drain#2 to fill fermentor(Same
    > as before)
    > 8) Stop
    >
    > maybe I could put another process so that if a maximum mash
    > temperature or boiling temperature is reached then an alrm will
    > sound.
    >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the Subject and
    Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
    >
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2003-08-29 19:59
    Heh, ok. The words "Large boiler" mean something completely different from
    what you're doing. To those in the trade, "medium" starts around 1000 sq.
    ft. of heating surface.

    No worries though, at 240/20A you're well below any licensing requirements
    in BC. Couldn't say about other jurisdictions for sure but I'm doubtfull
    something like that would be licensed. If its for use in your own home, you
    don't even have to worry about electrical tickets (at least, not in BC).

    Just make sure you have some sort of safety devices like a second
    temperature sensor that would cut power to the coils. A fuse/breaker sized
    appropriately and some sort of low-fluid trip to shut it off.

    Remember, household fire insurance usually has a clause that negates
    coverage if the fire is caused by a non CSA/UL listed device.

    >
    Original Message
    > From: jjlwork [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=v5OZH_RkqcY0QGizcr5jf7N5oTAtuO-jYufij93ScIUuyK9yHB4mzJ8Xgm8dDGDmanw8p6Pu4mc]jjlwork@y...[/url
    > Sent: August 29, 2003 11:07 AM
    > To: basicstamps@yahoogroups.com
    > Subject: [noparse][[/noparse]basicstamps] Re: New guy looking for a quick fix
    >
    >
    > I would just like to add that this is not a pressurized sytem, there
    > are no air tight lids, the potential for accident id if I get a boil
    > over...could be an electrifying experience! However I can implemnt
    > some safety circuits.
    >
    >