I am working on a project where I need to control a sprinkler valve
rated at 24VAC .30 amps. BTW this is not a lawn watering project. I
would rather not have to use a Lawn Sprinkler controller or Lawn
light controller to provide power to the valve, but rather use the
power supply that the Stamp would be using. Would it be better to
have:

1. (Preferable to me) A DC supply for the Stamp and valve and convert
the DC to AC for the valve? Would I have to have a 24 VDC supply and
step it down for the stamp? How would you go about doing all of this?

or

2.An AC supply to run the valve and step it down and convert it to DC
for the stamp. How would I do this if this is better than #1?

Thnx Already

Harold Goodrich

Comments

  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 15:50
    I don't have a solution to this problem, but I would like to know
    how you solve it if you find answers other than on this group. I
    am/will be addressing a similar problem.

    Thanks
    Don

    --- In basicstamps@y..., "hgoodric" <hgoodric@y...> wrote:
    > I am working on a project where I need to control a sprinkler valve
    > rated at 24VAC .30 amps. BTW this is not a lawn watering project. I
    > would rather not have to use a Lawn Sprinkler controller or Lawn
    > light controller to provide power to the valve, but rather use the
    > power supply that the Stamp would be using. Would it be better to
    > have:
    >
    > 1. (Preferable to me) A DC supply for the Stamp and valve and
    convert
    > the DC to AC for the valve? Would I have to have a 24 VDC supply
    and
    > step it down for the stamp? How would you go about doing all of
    this?
    >
    > or
    >
    > 2.An AC supply to run the valve and step it down and convert it to
    DC
    > for the stamp. How would I do this if this is better than #1?
    >
    > Thnx Already
    >
    > Harold Goodrich
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 16:15
    Hi:

    Probably the easiest way is to use the stamp I/O pin to drive a relay whose
    contacts close the 24VAC through to the solenoid. Make sure the winding
    resistance is high and the current draw is about 15ma. There are several of
    these type relays in the Jameco catalog. You also need a reversed diode
    accross the windings to prevent reverse voltage destroying the stamp output
    pin. There is another method and that is to drive the relay with a UNL
    2803. This IC can sink (supply ground) for 1/2 anp per gate. and has a
    built in diode protection provided. Again drive the relay and let the relay
    contacts drive the AC load. If using the UNL2803 simply output a high on
    that stamp pin.

    Good Luck

    Eric Adams

    Original Message
    From: "hgoodric" <hgoodric@y...>
    To: <basicstamps@yahoogroups.com>
    Sent: Monday, May 06, 2002 10:35 AM
    Subject: [noparse][[/noparse]basicstamps] Sprinkler Valve Control


    > I am working on a project where I need to control a sprinkler valve
    > rated at 24VAC .30 amps. BTW this is not a lawn watering project. I
    > would rather not have to use a Lawn Sprinkler controller or Lawn
    > light controller to provide power to the valve, but rather use the
    > power supply that the Stamp would be using. Would it be better to
    > have:
    >
    > 1. (Preferable to me) A DC supply for the Stamp and valve and convert
    > the DC to AC for the valve? Would I have to have a 24 VDC supply and
    > step it down for the stamp? How would you go about doing all of this?
    >
    > or
    >
    > 2.An AC supply to run the valve and step it down and convert it to DC
    > for the stamp. How would I do this if this is better than #1?
    >
    > Thnx Already
    >
    > Harold Goodrich
    >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the Subject and
    Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 16:29
    I strongly suggest you go with the second route. AC/DC adapter or "wall wart"
    for the stamp -- it can regulate its own power the rest of the way. Then,
    separately, have a transformer bring the 120 down to 12 (AC). Let the stamp
    switch a relay on the 120 side, and you'll be switching a very small amount of
    current (30 mA plus losses in the transformer).

    Clark Hughes

    hgoodric wrote:
    >
    > I am working on a project where I need to control a sprinkler valve
    > rated at 24VAC .30 amps. BTW this is not a lawn watering project. I
    > would rather not have to use a Lawn Sprinkler controller or Lawn
    > light controller to provide power to the valve, but rather use the
    > power supply that the Stamp would be using. Would it be better to
    > have:
    >
    > 1. (Preferable to me) A DC supply for the Stamp and valve and convert
    > the DC to AC for the valve? Would I have to have a 24 VDC supply and
    > step it down for the stamp? How would you go about doing all of this?
    >
    > or
    >
    > 2.An AC supply to run the valve and step it down and convert it to DC
    > for the stamp. How would I do this if this is better than #1?
    >
    > Thnx Already
    >
    > Harold Goodrich
    >
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 16:57
    Thanks Eric. I realize that i need a relay in the system. What I want
    is one plug-in to the wall to run the whole system, whether that be a
    24VAC wall wart that I have to convert to power the basicstamp or
    something else. I apprecite your input though!!

    Thnx

    Harold Goodrich
    --- In basicstamps@y..., "Eric Adams" <hugs102@b...> wrote:
    > Hi:
    >
    > Probably the easiest way is to use the stamp I/O pin to drive a
    relay whose
    > contacts close the 24VAC through to the solenoid. Make sure the
    winding
    > resistance is high and the current draw is about 15ma. There are
    several of
    > these type relays in the Jameco catalog. You also need a reversed
    diode
    > accross the windings to prevent reverse voltage destroying the
    stamp output
    > pin. There is another method and that is to drive the relay with a
    UNL
    > 2803. This IC can sink (supply ground) for 1/2 anp per gate. and
    has a
    > built in diode protection provided. Again drive the relay and let
    the relay
    > contacts drive the AC load. If using the UNL2803 simply output a
    high on
    > that stamp pin.
    >
    > Good Luck
    >
    > Eric Adams
    >
    >
    Original Message
    > From: "hgoodric" <hgoodric@y...>
    > To: <basicstamps@y...>
    > Sent: Monday, May 06, 2002 10:35 AM
    > Subject: [noparse][[/noparse]basicstamps] Sprinkler Valve Control
    >
    >
    > > I am working on a project where I need to control a sprinkler
    valve
    > > rated at 24VAC .30 amps. BTW this is not a lawn watering project.
    I
    > > would rather not have to use a Lawn Sprinkler controller or Lawn
    > > light controller to provide power to the valve, but rather use the
    > > power supply that the Stamp would be using. Would it be better to
    > > have:
    > >
    > > 1. (Preferable to me) A DC supply for the Stamp and valve and
    convert
    > > the DC to AC for the valve? Would I have to have a 24 VDC supply
    and
    > > step it down for the stamp? How would you go about doing all of
    this?
    > >
    > > or
    > >
    > > 2.An AC supply to run the valve and step it down and convert it
    to DC
    > > for the stamp. How would I do this if this is better than #1?
    > >
    > > Thnx Already
    > >
    > > Harold Goodrich
    > >
    > >
    > > To UNSUBSCRIBE, just send mail to:
    > > basicstamps-unsubscribe@y...
    > > from the same email address that you subscribed. Text in the
    Subject and
    > Body of the message will be ignored.
    > >
    > >
    > > Your use of Yahoo! Groups is subject to
    http://docs.yahoo.com/info/terms/
    > >
    > >
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 18:49
    FYI,

    The Darlington is a ULN2803, not a UNL2803.

    Larry Woods

    >
    Original Message
    > From: hgoodric [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=pnE_x6WMNF12Z6ZVAC6pr7ZcjqisIZV5junT84heeD440uup1WdJuQWsjdHf4qY5eOF2vOJ15d0Ao79U]hgoodric@y...[/url
    > Sent: Monday, May 06, 2002 8:57 AM
    > To: basicstamps@yahoogroups.com
    > Subject: [noparse][[/noparse]basicstamps] Re: Sprinkler Valve Control
    >
    >
    > Thanks Eric. I realize that i need a relay in the
    > system. What I want
    > is one plug-in to the wall to run the whole system,
    > whether that be a
    > 24VAC wall wart that I have to convert to power the
    > basicstamp or
    > something else. I apprecite your input though!!
    >
    > Thnx
    >
    > Harold Goodrich
    > --- In basicstamps@y..., "Eric Adams" <hugs102@b...> wrote:
    > > Hi:
    > >
    > > Probably the easiest way is to use the stamp I/O pin
    > to drive a
    > relay whose
    > > contacts close the 24VAC through to the solenoid.
    > Make sure the
    > winding
    > > resistance is high and the current draw is about
    > 15ma. There are
    > several of
    > > these type relays in the Jameco catalog. You also
    > need a reversed
    > diode
    > > accross the windings to prevent reverse voltage
    > destroying the
    > stamp output
    > > pin. There is another method and that is to drive
    > the relay with a
    > UNL
    > > 2803. This IC can sink (supply ground) for 1/2 anp
    > per gate. and
    > has a
    > > built in diode protection provided. Again drive the
    > relay and let
    > the relay
    > > contacts drive the AC load. If using the UNL2803
    > simply output a
    > high on
    > > that stamp pin.
    > >
    > > Good Luck
    > >
    > > Eric Adams
    > >
    > >
    Original Message
    > > From: "hgoodric" <hgoodric@y...>
    > > To: <basicstamps@y...>
    > > Sent: Monday, May 06, 2002 10:35 AM
    > > Subject: [noparse][[/noparse]basicstamps] Sprinkler Valve Control
    > >
    > >
    > > > I am working on a project where I need to control
    > a sprinkler
    > valve
    > > > rated at 24VAC .30 amps. BTW this is not a lawn
    > watering project.
    > I
    > > > would rather not have to use a Lawn Sprinkler
    > controller or Lawn
    > > > light controller to provide power to the valve,
    > but rather use the
    > > > power supply that the Stamp would be using. Would
    > it be better to
    > > > have:
    > > >
    > > > 1. (Preferable to me) A DC supply for the Stamp
    > and valve and
    > convert
    > > > the DC to AC for the valve? Would I have to have a
    > 24 VDC supply
    > and
    > > > step it down for the stamp? How would you go about
    > doing all of
    > this?
    > > >
    > > > or
    > > >
    > > > 2.An AC supply to run the valve and step it down
    > and convert it
    > to DC
    > > > for the stamp. How would I do this if this is
    > better than #1?
    > > >
    > > > Thnx Already
    > > >
    > > > Harold Goodrich
    > > >
    > > >
    > > > To UNSUBSCRIBE, just send mail to:
    > > > basicstamps-unsubscribe@y...
    > > > from the same email address that you subscribed.
    > Text in the
    > Subject and
    > > Body of the message will be ignored.
    > > >
    > > >
    > > > Your use of Yahoo! Groups is subject to
    > http://docs.yahoo.com/info/terms/
    > > >
    > > >
    >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text
    > in the Subject and Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to
    http://docs.yahoo.com/info/terms/
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 18:54
    A control valve that is rated for 24VAC will work fine on 24 VDC.
    However a Valve specified for 24VDC will not work, without a rectifier,
    on 24 VAC. I would use a 7404 inverter with the input pin to the stamp
    and it's output to a 2n3055 or similar power transistor to control the
    valve. A 2n2222 or a 2n3904 mike also work, but may be pushing the
    envelope of it's max. Ic current. A resistor from the inverter's output
    would be required from the inverter to the base of the transistor.

    HTH,

    Leroy

    hgoodric wrote:
    >
    > I am working on a project where I need to control a sprinkler valve
    > rated at 24VAC .30 amps. BTW this is not a lawn watering project. I
    > would rather not have to use a Lawn Sprinkler controller or Lawn
    > light controller to provide power to the valve, but rather use the
    > power supply that the Stamp would be using. Would it be better to
    > have:
    >
    > 1. (Preferable to me) A DC supply for the Stamp and valve and convert
    > the DC to AC for the valve? Would I have to have a 24 VDC supply and
    > step it down for the stamp? How would you go about doing all of this?
    >
    > or
    >
    > 2.An AC supply to run the valve and step it down and convert it to DC
    > for the stamp. How would I do this if this is better than #1?
    >
    > Thnx Already
    >
    > Harold Goodrich
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the Subject and Body
    of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 19:18
    At 13:54 05/06/02, Leroy Hall wrote:

    >A control valve that is rated for 24VAC will work fine on 24 VDC.
    >However a Valve specified for 24VDC will not work, without a rectifier,
    >on 24 VAC. I would use a 7404 inverter with the input pin to the stamp
    >and it's output to a 2n3055 or similar power transistor to control the
    >valve. A 2n2222 or a 2n3904 mike also work, but may be pushing the
    >envelope of it's max. Ic current. A resistor from the inverter's output
    >would be required from the inverter to the base of the transistor.

    I'd be *very* concerned that a solenoid meant to operate on AC would
    overheat severely if operated using DC. The reactance of the coil is a
    fair part of what limits current thru the coil when it is activated. If
    you use DC, then you only have the coil resistance to limit current and
    excessive current will flow.


    Jim H
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 19:26
    Harold,

    I am currently controlling 4 valves on one 24Vac power supply rated to
    handle all of the valves at the same time. However, I am only letting 3
    come on at a time if need be. I am taking the excess supply to run a
    Pic16F84A processor and various other electronics.

    I used a bridge rectifier and to get the DC then went from their with
    other components to get what I needed for the Pic.

    Brian G.
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 19:33
    In a message dated 5/6/02 12:55:32 PM Central Daylight Time, leroy@f...
    writes:


    >

    It's not a good idea to run AC valves on DC for long periods of time. The
    solenoid plunger tends to magnetize and attract ferrous bits that invariably
    float through the water, eventually causing the valve to fail -- usually open.

    -- Jon Williams


    [noparse][[/noparse]Non-text portions of this message have been removed]
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 19:40
    couldn't you just use a mosfet to turn off the ac to the valve ?


    richard



    Original Message
    From: <jonwms@a...>
    To: <basicstamps@yahoogroups.com>
    Sent: Monday, May 06, 2002 1:33 PM
    Subject: Re: [noparse][[/noparse]basicstamps] Sprinkler Valve Control


    > In a message dated 5/6/02 12:55:32 PM Central Daylight Time,
    leroy@f...
    > writes:
    >
    >
    > >
    >
    > It's not a good idea to run AC valves on DC for long periods of time. The
    > solenoid plunger tends to magnetize and attract ferrous bits that
    invariably
    > float through the water, eventually causing the valve to fail -- usually
    open.
    >
    > -- Jon Williams
    >
    >
    > [noparse][[/noparse]Non-text portions of this message have been removed]
    >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the Subject and
    Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 20:27
    Brian Garcia:

    So what bridge rectifier did you use?

    Thnx
    HG

    --- In basicstamps@y..., Brian Gracia <bgracia@b...> wrote:
    > Harold,
    >
    > I am currently controlling 4 valves on one 24Vac power supply rated
    to
    > handle all of the valves at the same time. However, I am only
    letting 3
    > come on at a time if need be. I am taking the excess supply to run
    a
    > Pic16F84A processor and various other electronics.
    >
    > I used a bridge rectifier and to get the DC then went from their
    with
    > other components to get what I needed for the Pic.
    >
    > Brian G.
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 20:53
    There is nothing wrong with powering the Stamp off of the 24ac transformer.
    I do this all the time with HVAC controls.
    A bridge, cap, regulator and you are in business. I use Optoisolators that
    the stamp can control and the output is a triac that can control the 24ac
    for the valve. The isolation is safe.

    Kirk Wasson

    Original Message
    From: J. Clark Hughes [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=nNMIgqsv7BGaIMRRllZ4OroHySo-vJKj2DSI55p6iVU5rGt4QX2YRSNVV__pGLM6DtLYcjNma4aChZB9FEhDEp58]jchughes@a...[/url
    Sent: Monday, May 06, 2002 10:30 AM
    To: basicstamps@yahoogroups.com
    Subject: Re: [noparse][[/noparse]basicstamps] Sprinkler Valve Control


    I strongly suggest you go with the second route. AC/DC adapter or "wall
    wart"
    for the stamp -- it can regulate its own power the rest of the way. Then,
    separately, have a transformer bring the 120 down to 12 (AC). Let the stamp
    switch a relay on the 120 side, and you'll be switching a very small amount
    of
    current (30 mA plus losses in the transformer).

    Clark Hughes

    hgoodric wrote:
    >
    > I am working on a project where I need to control a sprinkler valve
    > rated at 24VAC .30 amps. BTW this is not a lawn watering project. I
    > would rather not have to use a Lawn Sprinkler controller or Lawn
    > light controller to provide power to the valve, but rather use the
    > power supply that the Stamp would be using. Would it be better to
    > have:
    >
    > 1. (Preferable to me) A DC supply for the Stamp and valve and convert
    > the DC to AC for the valve? Would I have to have a 24 VDC supply and
    > step it down for the stamp? How would you go about doing all of this?
    >
    > or
    >
    > 2.An AC supply to run the valve and step it down and convert it to DC
    > for the stamp. How would I do this if this is better than #1?
    >
    > Thnx Already
    >
    > Harold Goodrich
    >

    To UNSUBSCRIBE, just send mail to:
    basicstamps-unsubscribe@yahoogroups.com
    from the same email address that you subscribed. Text in the Subject and
    Body of the message will be ignored.


    Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 21:00
    Kirk, Could you email me your circuit and which components you used?
    I am going to place an order from digikey soon and I would like to
    get the nec. parts. hgoodric@y...

    Thnx very much!!!

    HG

    --- In basicstamps@y..., "WASSON, KIRK D" <kwasson@e...> wrote:
    > There is nothing wrong with powering the Stamp off of the 24ac
    transformer.
    > I do this all the time with HVAC controls.
    > A bridge, cap, regulator and you are in business. I use
    Optoisolators that
    > the stamp can control and the output is a triac that can control
    the 24ac
    > for the valve. The isolation is safe.
    >
    > Kirk Wasson
    >
    >
    Original Message
    > From: J. Clark Hughes [noparse][[/noparse]mailto:jchughes@a...]
    > Sent: Monday, May 06, 2002 10:30 AM
    > To: basicstamps@y...
    > Subject: Re: [noparse][[/noparse]basicstamps] Sprinkler Valve Control
    >
    >
    > I strongly suggest you go with the second route. AC/DC adapter
    or "wall
    > wart"
    > for the stamp -- it can regulate its own power the rest of the
    way. Then,
    > separately, have a transformer bring the 120 down to 12 (AC). Let
    the stamp
    > switch a relay on the 120 side, and you'll be switching a very
    small amount
    > of
    > current (30 mA plus losses in the transformer).
    >
    > Clark Hughes
    >
    > hgoodric wrote:
    > >
    > > I am working on a project where I need to control a sprinkler
    valve
    > > rated at 24VAC .30 amps. BTW this is not a lawn watering project.
    I
    > > would rather not have to use a Lawn Sprinkler controller or Lawn
    > > light controller to provide power to the valve, but rather use the
    > > power supply that the Stamp would be using. Would it be better to
    > > have:
    > >
    > > 1. (Preferable to me) A DC supply for the Stamp and valve and
    convert
    > > the DC to AC for the valve? Would I have to have a 24 VDC supply
    and
    > > step it down for the stamp? How would you go about doing all of
    this?
    > >
    > > or
    > >
    > > 2.An AC supply to run the valve and step it down and convert it
    to DC
    > > for the stamp. How would I do this if this is better than #1?
    > >
    > > Thnx Already
    > >
    > > Harold Goodrich
    > >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@y...
    > from the same email address that you subscribed. Text in the
    Subject and
    > Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to
    http://docs.yahoo.com/info/terms/
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-06 23:36
    I had good success with providing battery power to the Stamp, 24V AC
    transformer for the valve switched via Radio Shack 275-310 solid
    state relay. Drive the SSR through a current limiting resistor and
    you're done. Let the Stamp SLEEP most of the time to extend battery
    life.

    Regards,

    Steve

    hgoodric wrote:

    > I am working on a project where I need to control a sprinkler valve
    > rated at 24VAC .30 amps...
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-07 00:04
    Getting a little dislexic ... but it works great


    Original Message
    From: "Larry Woods" <larry@l...>
    To: <basicstamps@yahoogroups.com>
    Sent: Monday, May 06, 2002 1:49 PM
    Subject: RE: [noparse][[/noparse]basicstamps] Re: Sprinkler Valve Control


    > FYI,
    >
    > The Darlington is a ULN2803, not a UNL2803.
    >
    > Larry Woods
    >
    > >
    Original Message
    > > From: hgoodric [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=KdLmwMF4lPgb038WcgY-Ytr56wSDAGMG_ztF6rqsT5UirzKLEsR0CmUCGCx0S2VhSsGrUFWlKpS9wg]hgoodric@y...[/url
    > > Sent: Monday, May 06, 2002 8:57 AM
    > > To: basicstamps@yahoogroups.com
    > > Subject: [noparse][[/noparse]basicstamps] Re: Sprinkler Valve Control
    > >
    > >
    > > Thanks Eric. I realize that i need a relay in the
    > > system. What I want
    > > is one plug-in to the wall to run the whole system,
    > > whether that be a
    > > 24VAC wall wart that I have to convert to power the
    > > basicstamp or
    > > something else. I apprecite your input though!!
    > >
    > > Thnx
    > >
    > > Harold Goodrich
    > > --- In basicstamps@y..., "Eric Adams" <hugs102@b...> wrote:
    > > > Hi:
    > > >
    > > > Probably the easiest way is to use the stamp I/O pin
    > > to drive a
    > > relay whose
    > > > contacts close the 24VAC through to the solenoid.
    > > Make sure the
    > > winding
    > > > resistance is high and the current draw is about
    > > 15ma. There are
    > > several of
    > > > these type relays in the Jameco catalog. You also
    > > need a reversed
    > > diode
    > > > accross the windings to prevent reverse voltage
    > > destroying the
    > > stamp output
    > > > pin. There is another method and that is to drive
    > > the relay with a
    > > UNL
    > > > 2803. This IC can sink (supply ground) for 1/2 anp
    > > per gate. and
    > > has a
    > > > built in diode protection provided. Again drive the
    > > relay and let
    > > the relay
    > > > contacts drive the AC load. If using the UNL2803
    > > simply output a
    > > high on
    > > > that stamp pin.
    > > >
    > > > Good Luck
    > > >
    > > > Eric Adams
    > > >
    > > >
    Original Message
    > > > From: "hgoodric" <hgoodric@y...>
    > > > To: <basicstamps@y...>
    > > > Sent: Monday, May 06, 2002 10:35 AM
    > > > Subject: [noparse][[/noparse]basicstamps] Sprinkler Valve Control
    > > >
    > > >
    > > > > I am working on a project where I need to control
    > > a sprinkler
    > > valve
    > > > > rated at 24VAC .30 amps. BTW this is not a lawn
    > > watering project.
    > > I
    > > > > would rather not have to use a Lawn Sprinkler
    > > controller or Lawn
    > > > > light controller to provide power to the valve,
    > > but rather use the
    > > > > power supply that the Stamp would be using. Would
    > > it be better to
    > > > > have:
    > > > >
    > > > > 1. (Preferable to me) A DC supply for the Stamp
    > > and valve and
    > > convert
    > > > > the DC to AC for the valve? Would I have to have a
    > > 24 VDC supply
    > > and
    > > > > step it down for the stamp? How would you go about
    > > doing all of
    > > this?
    > > > >
    > > > > or
    > > > >
    > > > > 2.An AC supply to run the valve and step it down
    > > and convert it
    > > to DC
    > > > > for the stamp. How would I do this if this is
    > > better than #1?
    > > > >
    > > > > Thnx Already
    > > > >
    > > > > Harold Goodrich
    > > > >
    > > > >
    > > > > To UNSUBSCRIBE, just send mail to:
    > > > > basicstamps-unsubscribe@y...
    > > > > from the same email address that you subscribed.
    > > Text in the
    > > Subject and
    > > > Body of the message will be ignored.
    > > > >
    > > > >
    > > > > Your use of Yahoo! Groups is subject to
    > > http://docs.yahoo.com/info/terms/
    > > > >
    > > > >
    > >
    > >
    > > To UNSUBSCRIBE, just send mail to:
    > > basicstamps-unsubscribe@yahoogroups.com
    > > from the same email address that you subscribed. Text
    > > in the Subject and Body of the message will be ignored.
    > >
    > >
    > > Your use of Yahoo! Groups is subject to
    > http://docs.yahoo.com/info/terms/
    >
    >
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the Subject and
    Body of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
    >
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2002-05-08 03:26
    The safest way to control AC Stiff with a Stamp is to use a solid state relay
    (or a mechanical one) to isolate the AC from the DC.

    You can use the same 24 VAC transformer to run the DC 5 volt regulator power
    supply to the Stamp.
    I use this method in the Flame Cutting Machines I rebuild. I use lots of ASCO
    Valves 24 and 120 VAC types. I have run 24 of them from 1 Stamp without a
    failure (going on 4 years now).

    When I get back to the office (in a few weeks) I can send you a pdf file of
    the schematic I use for this type of solenoid control. I use the valves to
    control Air, Acetylene Gas, Oxygen, Water and Nitrogen. The ASCO valves are
    about $100 each, but they are worth it when figuring in the damage a
    failed/leaky solenoid can cause.

    Thanks,
    Alan Bradford
    Plasma Technologies