On Fri, 14 Jul 2000, steve tatum wrote:

> Hello all,
> I'm working on an application that involves sequencing HVAC systems
> on a train. By this I mean that they can not all turn on at once b/c
> of the inrush current. There is one BSII controller per unit and I
> have 28 units (one unit per train car). I am using an RS485 data
> loop.
>
> Now here's the problem. I can't network
> using "Larry", "Curly", "Moe" or the "ping", "pong" topology that is
> described in the manuals b/c the "nodes" will be taken out of service
> and replaced with a new node that is not in any of the original 27
> (28-1=27) unit's program. Reprogramming the original 27 with this
> new node is not feasible. For the same reasons a master/slave
> network cannot be implemented either.
>

Why not assign each car's stamp with an address for that car and let the
units communicate using their addresses. You could have a "key" ( hard
wired header to simulate a dip switch pack ) that plugged into the unit in
each car that assigned the stamp an address upon power up. If you needed
to change out a stamp, the new one would assign itself the correct address
for that car upon power up after reading the "key". We used this back in
the early 80's to configure the controller boards in our network nodes.

Just a thought,


Dale Harwood [noparse][[/noparse] N4VFF ]

internet> dale@h...

ax.25> n4vff@n4vff.#cha.tn.usa.noam

#include <std_disclaimer.h>

Comments

  • ArchiverArchiver Posts: 46,084
    edited 2000-07-14 02:34
    Hello all,
    I'm working on an application that involves sequencing HVAC systems
    on a train. By this I mean that they can not all turn on at once b/c
    of the inrush current. There is one BSII controller per unit and I
    have 28 units (one unit per train car). I am using an RS485 data
    loop.

    Now here's the problem. I can't network
    using "Larry", "Curly", "Moe" or the "ping", "pong" topology that is
    described in the manuals b/c the "nodes" will be taken out of service
    and replaced with a new node that is not in any of the original 27
    (28-1=27) unit's program. Reprogramming the original 27 with this
    new node is not feasible. For the same reasons a master/slave
    network cannot be implemented either.

    I am trying to implement a "broadcast" type network. Meaning that,
    let's say, node 1 would send the $FF serial output to alert any other
    nodes listening that it is about to turn on its HVAC. The other
    nodes would be Polling periodically, timing out if no data is on the
    line and continuing with the program. However, this does leave a
    window of opportunity for another HVAC to turn on when a node is not
    listening and therefore they could both turn on at the same time.
    Would the flow control pin be the answer?? What if the other nodes
    are not listening at that particular time when you pulse the fpin??
    What happens if several nodes try to transmit data at the same time.

    An interrupt would solve the problem, but I do not believe that the
    BSII this capability.

    Any ideas out there??
  • ArchiverArchiver Posts: 46,084
    edited 2000-07-14 03:24
    At 01:34 AM 7/14/00, you wrote:
    >Hello all,
    >I'm working on an application that involves sequencing HVAC systems
    >on a train. By this I mean that they can not all turn on at once b/c
    >of the inrush current. There is one BSII controller per unit and I
    >have 28 units (one unit per train car). I am using an RS485 data
    >loop.
    >
    >Now here's the problem. I can't network
    >using "Larry", "Curly", "Moe" or the "ping", "pong" topology that is
    >described in the manuals b/c the "nodes" will be taken out of service
    >and replaced with a new node that is not in any of the original 27
    >(28-1=27) unit's program. Reprogramming the original 27 with this
    >new node is not feasible. For the same reasons a master/slave
    >network cannot be implemented either.
    >
    >I am trying to implement a "broadcast" type network. Meaning that,
    >let's say, node 1 would send the $FF serial output to alert any other
    >nodes listening that it is about to turn on its HVAC. The other
    >nodes would be Polling periodically, timing out if no data is on the
    >line and continuing with the program. However, this does leave a
    >window of opportunity for another HVAC to turn on when a node is not
    >listening and therefore they could both turn on at the same time.
    >Would the flow control pin be the answer?? What if the other nodes
    >are not listening at that particular time when you pulse the fpin??
    >What happens if several nodes try to transmit data at the same time.
    >
    >An interrupt would solve the problem, but I do not believe that the
    >BSII this capability.
    >
    >Any ideas out there??
    >
    >

    Hi Steve -

    Take a look at the S.N.A.P. protocol [noparse][[/noparse] www.hth.com/snap/ ] . It is a
    freeware, open,
    scalable, networking protocol originally developed for use with the PLM24
    system which can be found at the same web site [noparse][[/noparse] ... (as above) /PLM24/ ] .
    It adapts very nicely to other uses.

    A small subset of this protocol might be exactly what you are looking for.
    Examples, suggestions, complete documentation, as well as code segments are
    all downloadable from that site. This is also the home site of L.O.S.A.
    which is the List Of Stamp Applications, an effort HTH to provide a place
    for documenting Stamp Applications [noparse][[/noparse] www.hth.com/losa/ ] .

    Hope that helps.

    Regards,

    Bruce Bates
  • ArchiverArchiver Posts: 46,084
    edited 2000-07-14 04:41
    When you talk about a "broadcast" type network, I get the impression that
    you are thinking about one where the data lines are in parallel (i.e. all
    nodes get the data at the same time). What if the data were serialized,
    using a token based topology?

    Here's my idea:

    When a unit wants to turn on its HVAC, it sends out a token corresponding to
    its unique number (1,2,3,etc).
    The token gets passed from one node to another in the chain.
    Once the token comes back, the unit turns its HVAC on.

    Case where another unit wants to turn its HVAC when another unit is already
    sending around a token:
    If a unit receives a token while waiting for its own token to arrive, it
    compares the token received to itself. If the received token is less in
    priority (you decide what constitutes less priority), it will discard the
    incoming token. Each unit would have a specifed time out waiting for its
    token before sending out another token.

    Case where the unit turns its HVAC on and waiting for inrush to die down:
    In this mode, unit will indescriminately discard ALL tokens until specified
    time when in-rush has died down.

    One of the advantages I see is that this system is scalable. Also, worst
    case scenerio is that if a unit is not "listening" when it receives a token,
    the original unit wont turn its HVAC on (fail safe). However, there may be
    some unique logic situations I may be missing, so be sure to step through
    this carefully.

    Also, I am a newbie to Basic Stamp programming, so I am unsure how this
    would be implemented.

    Hope this helps..

    --Craig

    Original Message
    From: steve tatum [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=TilB6lXI6XH-4N76ZdyetVMy2bSARZLNk1o2hbkgwjlwXortzU5UJ7NEqdvQ44v1t6NjUgWoKsQW4j0]swt@p...[/url
    Sent: Thursday, July 13, 2000 9:35 PM
    To: basicstamps@egroups.com
    Subject: [noparse][[/noparse]basicstamps] BSII Networking


    Hello all,
    I'm working on an application that involves sequencing HVAC systems
    on a train. By this I mean that they can not all turn on at once b/c
    of the inrush current. There is one BSII controller per unit and I
    have 28 units (one unit per train car). I am using an RS485 data
    loop.

    Now here's the problem. I can't network
    using "Larry", "Curly", "Moe" or the "ping", "pong" topology that is
    described in the manuals b/c the "nodes" will be taken out of service
    and replaced with a new node that is not in any of the original 27
    (28-1=27) unit's program. Reprogramming the original 27 with this
    new node is not feasible. For the same reasons a master/slave
    network cannot be implemented either.

    I am trying to implement a "broadcast" type network. Meaning that,
    let's say, node 1 would send the $FF serial output to alert any other
    nodes listening that it is about to turn on its HVAC. The other
    nodes would be Polling periodically, timing out if no data is on the
    line and continuing with the program. However, this does leave a
    window of opportunity for another HVAC to turn on when a node is not
    listening and therefore they could both turn on at the same time.
    Would the flow control pin be the answer?? What if the other nodes
    are not listening at that particular time when you pulse the fpin??
    What happens if several nodes try to transmit data at the same time.

    An interrupt would solve the problem, but I do not believe that the
    BSII this capability.

    Any ideas out there??
  • ArchiverArchiver Posts: 46,084
    edited 2000-07-14 09:51
    On 14 Jul 00 at 1:34, steve tatum wrote:

    > ...I'm working on an application that involves sequencing HVAC
    > systems on a train. By this I mean that they can not all turn on
    > at once b/c of the inrush current. There is one BSII controller
    > per unit and I have 28 units (one unit per train car). I am using
    > an RS485 data loop... Any ideas out there??

    An intriguing problem. Here's a concept-level potential solution you
    may wish to consider and develop:

    - Give each of your Stamps a unique number ID in EEPROM (DATA
    statement) say from 1 to 30. Each Stamp's number remains the
    same regardless of its position or presence in the train.

    - After the cars are assembled, initialize your network to include
    determining the IDs of all Stamps on board. You could conceivably do
    this with a master that polls for Stamp #1, then #2, then #3 etc.
    - When polled, the Stamp answers back with its ID or the complement
    of its ID or whatever to announce its presence
    - After being polled, it listens to see which ID responds next, if
    any. It remembers which comes next (or, in the case of the last to
    respond, the first Stamp ID).

    - After initialization, the master could poll the Stamps in sequence
    to permit HVAC switching. Or, the master could be removed and the
    Stamps could do token-passing from then on to pass HVAC-switching
    permission from one to the next. The trick here would be effective
    token passing so it doesn't get dropped...

    Steve
  • ArchiverArchiver Posts: 46,084
    edited 2000-07-14 13:42
    On 14 Jul 00 at 20:45, Steve Tatum wrote:

    > I am new to token passing. Could you please send me a quick few
    > lines of code to give me an idea of how this works. I can't use
    > the master/slave topology b/c the master could be taken out of the
    > loop at any time.

    In this instance it could be described as simply taking turns, in a
    round robin fashion, at taking care of any required switch actions.
    The Stamp with the "token" is allowed to turn things on--all others
    must wait until they are passed the token.

    Imagine that Stamps #2, #5 and #8 are on the loop (I know your real
    requirement is larger, but this illustrates the point). During the
    initialization I described in the prior msg, it is known that Stamp
    #2 is the first (lowest numbered) on the network. It gets the token
    first. If it has switching to accomplish, it does so. Then it
    passes the token on to #5. #5 similarly does/doesn't switch as
    needed, then passes the token to #8. #8 does the same and passes the
    token back to #2, etc. It's a virtual token we're talking about.
    Controlling the passing of the token would be the crux of the
    problem.

    For starters in the example above, I'd try #2 broadcasting '5' on the
    net when #2 is ready to pass the token. Until it receives a '5' in
    reply (presumably from #5), it repeats sending '5'--#5 may have been
    busy doing other things and missed its queue. When #5 responds with
    '5', consider the token passed. To make the scheme more robust, add
    a timeout feature (e.g., #2 decides it's been too long since anybody
    passed the token, so it starts things over) or other error
    detection/correction goodies.

    FWIW, token passing is normally used to control which of several
    peers is allowed to transmit to the network at any time. This is
    much like your requirement, since it involves singular access to a
    common resource.

    Steve
  • ArchiverArchiver Posts: 46,084
    edited 2000-07-15 02:45
    I am new to token passing. Could you please send me a quick few lines of
    code to give me an idea of how this works. I can't use the master/slave
    topology b/c the master could be taken out of the loop at any time.

    Thankx for your help so far.

    Original Message
    From: S Parkis [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=27YJtwwwVYff7Z6GD6fjfQnXBAir8CDC-s2N2QtcmpITvvzv5D8npT-p3K2LLL7zLhmnnbS4NTGHsvgstBR8Og]parkiss@e...[/url
    Sent: Friday, July 14, 2000 3:52 AM
    To: steve tatum; basicstamps@egroups.com
    Subject: Re: [noparse][[/noparse]basicstamps] BSII Networking


    On 14 Jul 00 at 1:34, steve tatum wrote:

    > ...I'm working on an application that involves sequencing HVAC
    > systems on a train. By this I mean that they can not all turn on
    > at once b/c of the inrush current. There is one BSII controller
    > per unit and I have 28 units (one unit per train car). I am using
    > an RS485 data loop... Any ideas out there??

    An intriguing problem. Here's a concept-level potential solution you
    may wish to consider and develop:

    - Give each of your Stamps a unique number ID in EEPROM (DATA
    statement) say from 1 to 30. Each Stamp's number remains the
    same regardless of its position or presence in the train.

    - After the cars are assembled, initialize your network to include
    determining the IDs of all Stamps on board. You could conceivably do
    this with a master that polls for Stamp #1, then #2, then #3 etc.
    - When polled, the Stamp answers back with its ID or the complement
    of its ID or whatever to announce its presence
    - After being polled, it listens to see which ID responds next, if
    any. It remembers which comes next (or, in the case of the last to
    respond, the first Stamp ID).

    - After initialization, the master could poll the Stamps in sequence
    to permit HVAC switching. Or, the master could be removed and the
    Stamps could do token-passing from then on to pass HVAC-switching
    permission from one to the next. The trick here would be effective
    token passing so it doesn't get dropped...

    Steve
  • ArchiverArchiver Posts: 46,084
    edited 2000-07-15 06:27
    The token in my previous example would just be a bit stream that identified
    the unit (e.g. 0001 for 1, 1111 for 15). This bit stream would be passed
    from one unit to another, much like a "bucket brigade". Ever see how people
    put out fires without firetrucks and pumps - passing a bucket of water from
    one person to another?

    I can give you a quick pseudo-code example..

    Example with a total of three units: Each unit has a data in and data out
    pin. The pins of each unit would be wired to one another in series - e.g:
    Data out of unit 1 would be wired to data in of unit 2, Data out of unit 2
    would be wired to data in of unit 3, Data out of unit 3 would be wired to
    data in of unit 1; competing the circuit.

    If a unit wants to turn the HVAC on, it sends out its unique token on its
    data out pin.
    It waits for that token to return on its data in by polling its data in pin.
    When the token returns, the unit turns its HVAC on.

    When a unit is idle it polls for tokens on its data in pin
    When it receives a token it merely echos the data received onto its data out
    pin.

    Now, here is where the logic gets a little messy:
    If a unit has already sent a token and is waiting for its token to return,
    but receives a token from another unit.
    You could pass the token if it is a higher value than itself, but not pass
    it if it is lower or vice-versa depending on your application.

    If a unit has recently turned its HVAC on, the unit would not poll the data
    in pin for a preset time (until in-rush died down). Hence, any tokens
    passed at that time, would not get passed along in the chain; preventing
    another HVAC from turning on.

    Each unit would also have a preset timeout waiting for its token to return
    before retrying.




    No master slave relationship used here, and units can be pulled out and
    replaced at will - the only caveat here is that the data circuit can not be
    broken and each node must have a unique number.

    --Craig



    Original Message
    From: Steve Tatum [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=zPQ2e0bs4tUka2DBT7ZDj58rSmfR1TxRk_9Ck8tP5HYsA9N2pD6QvB--sAxd1H1qgDlN5mDZngQF57g]swt@p...[/url
    Sent: Friday, July 14, 2000 9:46 PM
    To: basicstamps@egroups.com
    Subject: RE: [noparse][[/noparse]basicstamps] BSII Networking
    Importance: High


    I am new to token passing. Could you please send me a quick few lines of
    code to give me an idea of how this works. I can't use the master/slave
    topology b/c the master could be taken out of the loop at any time.

    Thankx for your help so far.

    Original Message
    From: S Parkis [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=Pwl-lFVcvAnlu3LsgoK_a7_zC2ZVGNmDvic242Z-4icv4GpWtBdeZKa6QtD3A7nZw8DFraFIrpuZD6cJ]parkiss@e...[/url
    Sent: Friday, July 14, 2000 3:52 AM
    To: steve tatum; basicstamps@egroups.com
    Subject: Re: [noparse][[/noparse]basicstamps] BSII Networking


    On 14 Jul 00 at 1:34, steve tatum wrote:

    > ...I'm working on an application that involves sequencing HVAC
    > systems on a train. By this I mean that they can not all turn on
    > at once b/c of the inrush current. There is one BSII controller
    > per unit and I have 28 units (one unit per train car). I am using
    > an RS485 data loop... Any ideas out there??

    An intriguing problem. Here's a concept-level potential solution you
    may wish to consider and develop:

    - Give each of your Stamps a unique number ID in EEPROM (DATA
    statement) say from 1 to 30. Each Stamp's number remains the
    same regardless of its position or presence in the train.

    - After the cars are assembled, initialize your network to include
    determining the IDs of all Stamps on board. You could conceivably do
    this with a master that polls for Stamp #1, then #2, then #3 etc.
    - When polled, the Stamp answers back with its ID or the complement
    of its ID or whatever to announce its presence
    - After being polled, it listens to see which ID responds next, if
    any. It remembers which comes next (or, in the case of the last to
    respond, the first Stamp ID).

    - After initialization, the master could poll the Stamps in sequence
    to permit HVAC switching. Or, the master could be removed and the
    Stamps could do token-passing from then on to pass HVAC-switching
    permission from one to the next. The trick here would be effective
    token passing so it doesn't get dropped...

    Steve