Hi Everyone,

I'm wondering if there is a way i can determine if the grounded outlets in
my house are truly grounded? I recently bought a weller WES50 ESD safe
soldering iron as well as an ESD mat.

I ordered a device from newark, an Ideal industries(stat gard(61-038)),
which indicates if your ground is working, but the item is backordered and
unavailable for some time.

most all my work involves stamps, so hopefully this is not to off topic.

thanks

steve

Comments

  • ArchiverArchiver Posts: 46,084
    edited 2000-05-04 05:19
    Steve,

    Go to your local hardware store and pick up an outlet checker.
    It has three LEDs on it that will check wiring for proper layout.
    Its a pretty cheap item too.

    DLC

    sargent@s... wrote:
    >
    > Hi Everyone,
    >
    > I'm wondering if there is a way i can determine if the grounded outlets in
    > my house are truly grounded? I recently bought a weller WES50 ESD safe
    > soldering iron as well as an ESD mat.
    >
    > I ordered a device from newark, an Ideal industries(stat gard(61-038)),
    > which indicates if your ground is working, but the item is backordered and
    > unavailable for some time.
    >
    > most all my work involves stamps, so hopefully this is not to off topic.
    >
    > thanks
    >
    > steve

    --
    Dennis Clark http://www.verinet.com/~dlc
    dlc@v...
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-04 06:11
    At 10:11 PM 5/3/00 -0500, sargent@s... wrote:

    >Hi Everyone,
    >
    >I'm wondering if there is a way i can determine if the grounded outlets in
    >my house are truly grounded? I recently bought a weller WES50 ESD safe
    >soldering iron as well as an ESD mat.
    >
    >I ordered a device from newark, an Ideal industries(stat gard(61-038)),
    >which indicates if your ground is working, but the item is backordered and
    >unavailable for some time.
    >
    >most all my work involves stamps, so hopefully this is not to off topic.
    >
    >thanks
    >
    >steve

    Run to your nearest hardware store and purchase one of those little outlet
    testers. It will have 3 lights on it - when it is plugged into a properly
    wired and grounded outlet, two of the lights are lit and the last is
    out. There are other more expensive versions that will actually pass a
    brief but substantial pulse into the ground and provide a very good
    indication of the quality of ground but you may not need this.

    If you are competent to handle 120 VAC wiring without injuring yourself,
    you can test it yourself. You will need a 60W to 100W lamp (standard 120
    VAC) and suitable lamp base, a 3 conductor cord brought out to pigtails and
    a meter. The concept is simple - pass the lamp current from the HOT to the
    GROUND terminals and measure the voltage drop on the ground. But it
    involves dangerous voltages and you MUST be careful!

    All you do is wire the lamp between the BLACK and GREEN wires. Connect the
    meter between the WHITE and GREEN wires. Make sure that everything is
    insulated and won't touch anything or anybody. Plug in the cord. If the
    ground is OK, the lamp will light full brightness and you will measure less
    than 2 or 3 volts AC between the WHITE and GREEN wires. If the lamp does
    NOT light, you have problems and must have them dealt with.

    You can approximate the ground wire resistance by noting that the current
    drawn from the lamp causes the voltage differential between the ground and
    neutral lines (assuming that this is the only load on that branch
    circuit). Figure out how much current is flowing (I=P/V), then figure out
    the ground conductor resistance. Note that this measures the conductor
    (wire) resistance only.

    This test is simple and reliable. But it won't catch ground to neutral
    shorts and you have to be careful while performing the test.

    Hope this helps!

    dwayne



    Dwayne Reid <dwayner@p...>
    Trinity Electronics Systems Ltd Edmonton, AB, CANADA
    (780) 489-3199 voice (780) 487-6397 fax

    Celebrating 16 years of Engineering Innovation (1984 - 2000)

    * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * *
    Do NOT send unsolicited commercial email to this email address.
    This message neither grants consent to receive unsolicited
    commercial email nor is intended to solicit commercial email.
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-04 06:52
    At 10:11 PM 5/3/00 -0500, sargent@s... promulgated:
    >
    >Hi Everyone,
    >
    >I'm wondering if there is a way i can determine if the grounded outlets in
    >my house are truly grounded? I recently bought a weller WES50 ESD safe
    >soldering iron as well as an ESD mat.
    >
    >I ordered a device from newark, an Ideal industries(stat gard(61-038)),
    >which indicates if your ground is working, but the item is backordered and
    >unavailable for some time.
    >
    >most all my work involves stamps, so hopefully this is not to off topic.
    >
    >thanks
    >
    >steve

    Steve -

    As stated, the only way you can get an empirical test is with a continuity
    check on the earth ground vs. a known good external driven ground. If there
    is little difference between the two resistance readings, your ground
    circuit is complete.

    The instrument used to make these tests is a "Megger" (reads in megaohms).
    The device uses a very high voltage, very low current, very short duration
    pulse
    to make the test. It probably will exceed the voltage ratings of any wire
    in the
    path. That's fine - that is the intent of an earth ground to carry maximum
    voltage
    and current safely to ground. In a properly conditioned AC electrical
    system, this ground fault can be detected, and appropriate action will be
    taken (per NEC or other regulations). Not all systems require detection or
    action; often the solid ground path is adequate to meet the users
    requirement. That would seem to be the
    case here.

    Be happy to speak more about it offlist if you wish. I own a "Megger"
    (Amprobe)
    and would be happy to answer any other similar grounding questions. My
    expertise
    is NOT in ESD, but rather residential and commercial AC electrical systems,
    ground fault protection and grounding/bonding of said systems. Here those
    two topics meet.

    Regards,

    Bruce

    >
    >
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-04 16:19
    I feel that I have to jump in here. I agree with all that has been said BUT
    only by using a megger can you be truly sure that the neutral and ground
    have NOT been bonded together at some point. The 3 led device only sees that
    some wire that eventually goes to ground is connected to the ground screw.
    If someone at sometime at some point (other than the main panel) on your
    system , had tied the neutral and ground together, then you don't have a
    'good' ground and will be subject to problems with "transients" or "sneak
    currents".

    Dan

    Original Message
    From: Bruce Bates [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=qd4-Kd2aqPf0OpUCIzXjZNagjvgjF5nmp6f5fKtPDjn-67JSUpuGSCPHVpvbl5bAtKE2D63zRp6Rr7yMDCMawNbE6Lis_2BZ3wNesqM]bvbates@m...[/url
    Sent: Wednesday, May 03, 2000 11:52 PM
    To: basicstamps@egroups.com
    Subject: Re: [noparse][[/noparse]basicstamps] off topic

    At 10:11 PM 5/3/00 -0500, sargent@s... promulgated:
    >
    >Hi Everyone,
    >
    >I'm wondering if there is a way i can determine if the grounded outlets in
    >my house are truly grounded? I recently bought a weller WES50 ESD safe
    >soldering iron as well as an ESD mat.
    >
    >I ordered a device from newark, an Ideal industries(stat gard(61-038)),
    >which indicates if your ground is working, but the item is backordered and
    >unavailable for some time.
    >
    >most all my work involves stamps, so hopefully this is not to off topic.
    >
    >thanks
    >
    >steve

    Steve -

    As stated, the only way you can get an empirical test is with a continuity
    check on the earth ground vs. a known good external driven ground. If there
    is little difference between the two resistance readings, your ground
    circuit is complete.

    The instrument used to make these tests is a "Megger" (reads in megaohms).
    The device uses a very high voltage, very low current, very short duration
    pulse
    to make the test. It probably will exceed the voltage ratings of any wire
    in the
    path. That's fine - that is the intent of an earth ground to carry maximum
    voltage
    and current safely to ground. In a properly conditioned AC electrical
    system, this ground fault can be detected, and appropriate action will be
    taken (per NEC or other regulations). Not all systems require detection or
    action; often the solid ground path is adequate to meet the users
    requirement. That would seem to be the
    case here.

    Be happy to speak more about it offlist if you wish. I own a "Megger"
    (Amprobe)
    and would be happy to answer any other similar grounding questions. My
    expertise
    is NOT in ESD, but rather residential and commercial AC electrical systems,
    ground fault protection and grounding/bonding of said systems. Here those
    two topics meet.

    Regards,

    Bruce

    >
    >
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-04 19:42
    At 09:19 AM 5/4/00 -0600, Sherman, Dan wrote:
    >I feel that I have to jump in here. I agree with all that has been said BUT
    >only by using a megger can you be truly sure that the neutral and ground
    >have NOT been bonded together at some point. The 3 led device only sees that
    >some wire that eventually goes to ground is connected to the ground screw.
    >If someone at sometime at some point (other than the main panel) on your
    >system , had tied the neutral and ground together, then you don't have a
    >'good' ground and will be subject to problems with "transients" or "sneak
    >currents".

    I fail to see your reasoning. In fact, why use a Megger at all? A Megger
    is used to measure HIGH resistance values, not low (although modern units
    can measure low resistance values). But a standard Megger (like the
    original crank handle units) measures leakage and insulation resistance values.

    The neutral and ground wires are SUPPOSED to be connected together, but
    only at the main disconnect panel (the service entrance). The problem I
    was alluding to was where someone might have faked a grounded outlet in a
    location with only two conductor wiring by connecting the neutral wire to
    the ground terminal of the receptacle. Don't laugh - I have come across
    this several times.

    The Canadian Electrical Code (and its US counterpart - the National
    Electrical Code) require that the incoming neutral be bonded to both the
    casing of the meter socket as well as the main disconnect panel. These are
    in turn bonded together and to Earth ground.

    The bottom line, however, is that checking the quality of the ground
    conductor at the receptacle requires a low resistance measurement that is
    not affected by the presence of AC voltage.

    dwayne



    Dwayne Reid <dwayner@p...>
    Trinity Electronics Systems Ltd Edmonton, AB, CANADA
    (780) 489-3199 voice (780) 487-6397 fax

    Celebrating 16 years of Engineering Innovation (1984 - 2000)

    * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * *
    Do NOT send unsolicited commercial email to this email address.
    This message neither grants consent to receive unsolicited
    commercial email nor is intended to solicit commercial email.
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-04 20:29
    I have failed to get my point across.[noparse]:([/noparse] I agree completely with what you
    say. The megger is only one way. There are others, but the 3 led device is
    NOT one of them. If the neutral and ground are tied together anywhere but at
    the entrance panel, the 3 led device will show that the outlet is good even
    though there is still the potential for ground loops that can cause
    problems. (I don't write any better than I talk.;-)) (At least I think
    that this is what I wanted to say the first time.)

    Dan

    Original Message
    From: Dwayne Reid [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=sR0wMjMHJM9neCeNWiPMx-y8WZ_s-lXUl3sZKYe0bl6IE7_7Is5pc3XrJSyRp602h5JTcBCWg952U_KOnkWy9w]dwayner@p...[/url
    Sent: Thursday, May 04, 2000 12:43 PM
    To: basicstamps@egroups.com
    Subject: RE: [noparse][[/noparse]basicstamps] off topic

    At 09:19 AM 5/4/00 -0600, Sherman, Dan wrote:
    >I feel that I have to jump in here. I agree with all that has been said
    BUT
    >only by using a megger can you be truly sure that the neutral and ground
    >have NOT been bonded together at some point. The 3 led device only sees
    that
    >some wire that eventually goes to ground is connected to the ground screw.
    >If someone at sometime at some point (other than the main panel) on your
    >system , had tied the neutral and ground together, then you don't have a
    >'good' ground and will be subject to problems with "transients" or "sneak
    >currents".

    I fail to see your reasoning. In fact, why use a Megger at all? A Megger
    is used to measure HIGH resistance values, not low (although modern units
    can measure low resistance values). But a standard Megger (like the
    original crank handle units) measures leakage and insulation resistance
    values.

    The neutral and ground wires are SUPPOSED to be connected together, but
    only at the main disconnect panel (the service entrance). The problem I
    was alluding to was where someone might have faked a grounded outlet in a
    location with only two conductor wiring by connecting the neutral wire to
    the ground terminal of the receptacle. Don't laugh - I have come across
    this several times.

    The Canadian Electrical Code (and its US counterpart - the National
    Electrical Code) require that the incoming neutral be bonded to both the
    casing of the meter socket as well as the main disconnect panel. These are
    in turn bonded together and to Earth ground.

    The bottom line, however, is that checking the quality of the ground
    conductor at the receptacle requires a low resistance measurement that is
    not affected by the presence of AC voltage.

    dwayne



    Dwayne Reid <dwayner@p...>
    Trinity Electronics Systems Ltd Edmonton, AB, CANADA
    (780) 489-3199 voice (780) 487-6397 fax

    Celebrating 16 years of Engineering Innovation (1984 - 2000)

    * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * *
    Do NOT send unsolicited commercial email to this email address.
    This message neither grants consent to receive unsolicited
    commercial email nor is intended to solicit commercial email.
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-04 20:30
    Not laughing here Dwayne. I was conducting an electrical safety class at a
    fire station on an Air Force base. To demo the circuit from the black hot
    ac to the center (green) grounding wire with a lightbulb at the AC outlet,
    nothing happened. Low and behold the safety wire was never installed
    throughout the recently completed building. Talk about sparks flying and I
    don't mean electrical..... ==Mac==

    SNIP
    SNIP
    SNIP
    SNIP
    >The neutral and ground wires are SUPPOSED to be connected together, but
    >only at the main disconnect panel (the service entrance). The problem I
    >was alluding to was where someone might have faked a grounded outlet in a
    >location with only two conductor wiring by connecting the neutral wire to
    >the ground terminal of the receptacle. Don't laugh - I have come across
    >this several times.
    SNIP
    SNIP
    SNIP
    SNIP
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-05 02:04
    thanks to all for the comments,

    what I'm hoping to figure out is whether or not my "ESD" safe Iron and work
    mat
    are plugged into an outlet which will make them happy (providing a circuit
    to dissipate).

    It sounds as if there are two thoughts, one being is it grounded properly,
    the other is it grounded at all?

    for my purposes, how can I be sure my soldering iron isn't zapping my IC's?

    Thanks,

    steve
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-05 16:29
    At 08:04 PM 5/4/00 -0500, sargent@s... wrote:
    >thanks to all for the comments,
    >
    >what I'm hoping to figure out is whether or not my "ESD" safe Iron and work
    >mat
    >are plugged into an outlet which will make them happy (providing a circuit
    >to dissipate).
    >
    >It sounds as if there are two thoughts, one being is it grounded properly,
    >the other is it grounded at all?
    >
    >for my purposes, how can I be sure my soldering iron isn't zapping my IC's?
    >
    >Thanks,
    >
    >steve

    The little 3 light tester should be adequate for that purpose. The more
    complicated method I mentioned simply lets you know how good that ground
    is. This would be important if you were relying upon that ground for noise
    reduction or for handling fault currents.

    But it sounds like all you really need to do is ensure that the tip of the
    iron does not have a lot of voltage on it caused by leakage currents from
    the heating element or static electricity. The little tester will show if
    there is a ground path of some nature there - that's what you are looking for.

    dwayne



    Dwayne Reid <dwayner@p...>
    Trinity Electronics Systems Ltd Edmonton, AB, CANADA
    (780) 489-3199 voice (780) 487-6397 fax

    Celebrating 16 years of Engineering Innovation (1984 - 2000)

    * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * *
    Do NOT send unsolicited commercial email to this email address.
    This message neither grants consent to receive unsolicited
    commercial email nor is intended to solicit commercial email.
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-05 16:34
    When we pull a set of 500 MCM (or larger) to a motor control center or
    switch gear we put the megger on them. The megger tells us the wires are
    not shorted to earth gound , to each other, or to the grounded conductor
    (if there is one). That way when we energize them they don't go BOOM.

    If you take a Vol-Con or Wiggy (voltage meter with lites and inductive coil
    that vibrates when 120vac is applied) and hook probes to the nuetral (white)
    and ground (green) there shouldn't be any voltage. I have found alot
    of residental electrical systems are not hooked up correctly.

    Another way is to put a multimeter on the gound and nuetral, if it shows
    a couple volts or so, you know they are connected somewhere other
    than the service enterance.

    Fixing this is another story. You must locate and inspect every splice
    in the house.

    The thing that gets me is the inspectors never check for this kind of
    problem. Your house could pass inspection with flying colors, but
    not be wired correctly at all.

    Meggers are expensive and many people just don't have one laying
    around.

    Isolated ground outlets (orange with green triangle) help out with
    this problem. Their a whole nother story.

    Also - be careful when checking or testing 120VAC
    It has been know to jump out and bite people.

    kevink
  • ArchiverArchiver Posts: 46,084
    edited 2000-05-05 18:34
    Dwayne,

    thanks, that makes sense

    Steve




    At 09:29 AM 05/05/2000 -0600, you wrote:
    >At 08:04 PM 5/4/00 -0500, sargent@s... wrote:
    >>thanks to all for the comments,
    >>
    >>what I'm hoping to figure out is whether or not my "ESD" safe Iron and work
    >>mat
    >>are plugged into an outlet which will make them happy (providing a circuit
    >>to dissipate).
    >>
    >>It sounds as if there are two thoughts, one being is it grounded properly,
    >>the other is it grounded at all?
    >>
    >>for my purposes, how can I be sure my soldering iron isn't zapping my IC's?
    >>
    >>Thanks,
    >>
    >>steve
    >
    >The little 3 light tester should be adequate for that purpose. The more
    >complicated method I mentioned simply lets you know how good that ground
    >is. This would be important if you were relying upon that ground for noise
    >reduction or for handling fault currents.
    >
    >But it sounds like all you really need to do is ensure that the tip of the
    >iron does not have a lot of voltage on it caused by leakage currents from
    >the heating element or static electricity. The little tester will show if
    >there is a ground path of some nature there - that's what you are looking
    for.
    >
    >dwayne
    >
    >
    >
    >Dwayne Reid <dwayner@p...>
    >Trinity Electronics Systems Ltd Edmonton, AB, CANADA
    >(780) 489-3199 voice (780) 487-6397 fax
    >
    >Celebrating 16 years of Engineering Innovation (1984 - 2000)
    >
    >* * * * * * * * * * * * * * * * * * * * * * * * * * * * * * *
    >Do NOT send unsolicited commercial email to this email address.
    >This message neither grants consent to receive unsolicited
    >commercial email nor is intended to solicit commercial email.
    >
    >
    >
    >
  • ArchiverArchiver Posts: 46,084
    edited 2000-10-05 00:51
    sorry for the off topic post, figured someone here may be able to enlighten
    me.

    When i turned on my computer this evening and started Interner Explorer 5,
    I found that my start page had been changed, from www.google.com

    to www.sureseeker.com

    It makes me nervous that this was done automatically somehow?

    anyone ever run into this before?

    google has been my start page for over a year, then magically, it was changed?

    Steve

    p.s. I'm the only user of my computer, then again, maybe i just answered my
    own question, someone broke into my house to change my internet preferences?
  • ArchiverArchiver Posts: 46,084
    edited 2000-12-21 03:37
    I ran across an interesting photo today. I thought being the holidays and
    all..........

    http://antwrp.gsfc.nasa.gov/apod/image/0011/earthlights_dmsp.jpg

    A larger version of the photo, 600K at

    http://antwrp.gsfc.nasa.gov/apod/image/0011/earthlights_dmsp_big.jpg

    happy holidays,

    Steve
  • ArchiverArchiver Posts: 46,084
    edited 2000-12-21 12:48
    nice photos thanks for sharing

    Original Message
    From: sargent@s... [noparse]/noparse]mailto:[url=http://forums.parallaxinc.com/group/basicstamps/post?postID=Bcc6S1_bkg4ASv0mOvfGP6RYgMviU2Jb8aQIJvDxLH_um0YRQDqkPowuNXUjmW-1PI7mRcoFN6gBTYU]sargent@s...[/url
    Sent: Wednesday, December 20, 2000 10:38 PM
    To: basicstamps@egroups.com
    Subject: Re: [noparse][[/noparse]basicstamps] off topic


    I ran across an interesting photo today. I thought being the holidays and
    all..........

    http://antwrp.gsfc.nasa.gov/apod/image/0011/earthlights_dmsp.jpg

    A larger version of the photo, 600K at

    http://antwrp.gsfc.nasa.gov/apod/image/0011/earthlights_dmsp_big.jpg

    happy holidays,

    Steve
  • ArchiverArchiver Posts: 46,084
    edited 2002-02-25 16:40
    This is off topic! If anyone is familiar with networking? I'm
    just trying to connect two computers Using win 98 and two network
    cards. Please contact me off list.

    lgaminde@T...
  • ArchiverArchiver Posts: 46,084
    edited 2002-02-25 18:32
    Dear Larry,

    It's pretty simple really. You need a cable from each computer's
    network card to a "hub" a five or six port is probably the smallest you
    can get. They are cheap, especially used. Be nice if you could find one
    that would connect to your printer, other wise it will reside on one or
    the other computer's parallel port. Make sure you have the right drivers
    for your network cards. Latest ones are generally available at
    driver.com or the manufacture web site. Pick cables they will connect
    your cards to the hub you chose. I would recommend 100 MHZ cards
    although 10 MHZ will work in a home environment, long as you don't have
    to transfer files too large (> 10 mb). Make sure the speed of your hub
    will match your network cards. Windows ME has a wizard that will set up
    the software for you, if that is an option and if not read the doc's on
    networking in the windows 98 help files.

    Maybe you can locate a software junkie that can help you with the
    software set up, once the above hardware is connected.

    Hope this helps,

    Leroy

    Larry Gaminde wrote:
    >
    > This is off topic! If anyone is familiar with networking? I'm
    > just trying to connect two computers Using win 98 and two network
    > cards. Please contact me off list.
    >
    > lgaminde@T...
    >
    > To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    > from the same email address that you subscribed. Text in the Subject and Body
    of the message will be ignored.
    >
    >
    > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
  • ArchiverArchiver Posts: 46,084
    edited 2002-02-25 19:12
    Hi Larry,

    If the distance between PC's isn't to far (less than 50 feet) then you
    don't even need the hub in place. Connect directly from network card to
    network card using a crossover cable - it has to be a crossover cable in
    order to go directly from network card to network card. Otherwise go with
    Leroy's advice and use the hub with straight-through cables.

    Tim Medema

    At 01:32 PM 2/25/2002 -0500, you wrote:
    >Dear Larry,
    >
    >It's pretty simple really. You need a cable from each computer's
    >network card to a "hub" a five or six port is probably the smallest you
    >can get. They are cheap, especially used. Be nice if you could find one
    >that would connect to your printer, other wise it will reside on one or
    >the other computer's parallel port. Make sure you have the right drivers
    >for your network cards. Latest ones are generally available at
    >driver.com or the manufacture web site. Pick cables they will connect
    >your cards to the hub you chose. I would recommend 100 MHZ cards
    >although 10 MHZ will work in a home environment, long as you don't have
    >to transfer files too large (> 10 mb). Make sure the speed of your hub
    >will match your network cards. Windows ME has a wizard that will set up
    >the software for you, if that is an option and if not read the doc's on
    >networking in the windows 98 help files.
    >
    >Maybe you can locate a software junkie that can help you with the
    >software set up, once the above hardware is connected.
    >
    >Hope this helps,
    >
    >Leroy
    >
    >Larry Gaminde wrote:
    > >
    > > This is off topic! If anyone is familiar with networking? I'm
    > > just trying to connect two computers Using win 98 and two network
    > > cards. Please contact me off list.
    > >
    > > lgaminde@T...
    > >
    > > To UNSUBSCRIBE, just send mail to:
    > > basicstamps-unsubscribe@yahoogroups.com
    > > from the same email address that you subscribed. Text in the Subject
    > and Body of the message will be ignored.
    > >
    > >
    > > Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
    >
    >
    >To UNSUBSCRIBE, just send mail to:
    > basicstamps-unsubscribe@yahoogroups.com
    >from the same email address that you subscribed. Text in the Subject and
    >Body of the message will be ignored.
    >
    >
    >Your use of Yahoo! Groups is subject to http://docs.yahoo.com/info/terms/
Sign In or Register to comment.