Hi everyone, I am new here to your forum and have a question.
what im trying to do is start/stop a 220v ac single phase motor via proximity switch and relay. My question is if L1 of the 220v is continuously connected to the motor and the other L2 of the 220v (110v) is connected to the proximity switch, can I also use the same L2 to supply the 110v needed to supply power to the other side of the relay which would supply power to the motor when the proximity switch is made up?
«1

Comments

  • kwinnkwinn Posts: 8,697
    edited 2014-12-30 21:07
    You can connect it between Neutral and either L1 or L2 as shown in the attached diagram. The relay coil should NOT be connected to ground. The motor case should be grounded unless it is double insulated and has a plastic case.

    RELAY CONNECTION.jpg
    454 x 261 - 19K
  • mac44mac44 Posts: 10
    edited 2014-12-30 21:24
    so if I connect to neutral instead of ground, the way I have it drawn will work?
  • DomanikDomanik Posts: 233
    edited 2014-12-30 22:01
    Find an electrician.
  • Peter JakackiPeter Jakacki Posts: 10,193
    edited 2014-12-30 22:24
    WARNING!

    Everyone, be very careful about giving any kind of advice about this type of general mains wiring especially since the OP does not seem to have any understanding about this at all. One stupid mistake and it could come back on you. The fact that he hooked up the ground like he did has shocked me enough already. Delete your posts or at least give a warning about what not to do but don't say what should be done. You are all already saying it is dangerous, that is enough.
  • mac44mac44 Posts: 10
    edited 2014-12-30 22:42
    why dont you try being helpful Peter.
  • Peter JakackiPeter Jakacki Posts: 10,193
    edited 2014-12-30 22:49
    mac44 wrote: »
    why dont you try being helpful Peter.

    This is your first post and you are very new here and if you weren't you would know I am always very helpful, as are many of the forum members. What you are asking should not be permitted on the forum due not only to litigation but also to possible lose of life and limb. If you do not possess enough knowledge to know about the earth then even really good advice could be misinterpreted and misapplied. I don't want to be part of that and being helpful can make it very very easy for us to fall into that trap and the dark abyss of consequences.
  • mac44mac44 Posts: 10
    edited 2014-12-30 22:58
    If you dont want to be a part of it , then thats ok dont reply, but you also shouldnt try to get those who are trying to help and trying to tell me how to do it safely not to help me either!
  • DomanikDomanik Posts: 233
    edited 2014-12-30 23:56
    mac44 wrote: »
    If you dont want to be a part of it , then thats ok dont reply, but you also shouldnt try to get those who are trying to help and trying to tell me how to do it safely not to help me either!
    220VAC opens liability issues for the one giving advice. You should be talking to an electrician because it's obvious you don't have the proper background to do this work safely.
  • mac44mac44 Posts: 10
    edited 2014-12-31 00:14
    How else do you learn if you cant ask someone who knows?
  • LoopyBytelooseLoopyByteloose Posts: 12,537
    edited 2014-12-31 00:18
    While I have never felt particularly happy with electricians apparent monopoly of wiring AC, Peter J. is simply trying to make clear that DIY wiring of AC mains has serious safety issues.

    Just the proper selection of a relay is not simple. And the relay you are going to use is likely to be expensive if you are doing anything above 1/10th of a horsepower.

    It is not uncommon for new users to simply think that all switches will work safely with anything, that any size wire is appropriate, and that fuses are not really necessary.

    The reality is that once you start working with VAC at 220 or even 110 and 15 amps or more, you really have to be aware of safety issues, fire danger, and proper sizing of switching.

    Are you up to that? Can you at least tell us how many horsepower your AC motor is going to be? Everything else needs to be sized around that particular item.

    Above all, Safety First.

    You may locally have classes in a community college for proper wiring of AC mains. Mistakes can be fatal to you or people that use the devices you wire and presume you know what you are doing.

    Enabling misadventure over the internet is simply unwise. One doesn't have to justify it in terms of a potential legal liability. I'd hate to think my comments put anyone in the hospital or worse.
  • mac44mac44 Posts: 10
    edited 2014-12-31 00:30
    all I am doing is replacing an existing troublesome microswitch with a proximity switch. all of the wiring and motors are already there and were installed by an electrician. I made an error by putting "ground" instead of "neutral " on my drawing. I have replaced motors and a lot of wiring in my life mostly 120v though. I am a mechanic, not an electrician.
  • LoopyBytelooseLoopyByteloose Posts: 12,537
    edited 2014-12-31 00:49
    Well, a microswitch can actually be rated at 220VAC and 20 amps for safe operation, where the proximity switch you refer to can be a small device that only switches 5VDC in the range of milliamps.

    That pretty much is a case of either finding a packaged solution that drops in, or building the whole unit from scratch, including 5VDC power to the proximity switch.

    And of course, there are a whole range of proximity switches (ultrasonic devices, hall effect switches, etc.).

    I sounds as though you are pretty much in a conceptual stage of this project.
  • mac44mac44 Posts: 10
    edited 2014-12-31 01:01
    yes, I will be using a 90-240vac capacitive proximity switch and a 125vac 20amp relay with a 120vac coil so no DC power supply will be necessary.
  • LoopyBytelooseLoopyByteloose Posts: 12,537
    edited 2014-12-31 01:15
    Well, the microswitch could be failing due to poor design.

    It is not uncommon with inductive load switching to require 5x the steady load demand for a switch. So for a 20amp load, you might need a 100amp relay AND sophisticate snubbing circuitry to protect the relays switching.

    It all goes back to what size is the motor and what is the duty cycle that the switching is expected to perform. If you just cobble together something that is cheap and seems to work first time, it may soon fail.

    Of course, you might get lucky and have it all work quite well.

    Still seems that you want someone to validate a design and that does create a legal liability for that someone.

    EBay has something like you describe. http://www.ebay.com/itm/NEW-Omron-E2K-X15MY1-Capacitive-Proximity-Switch-Sensor-100-240vac-/390930880601

    But the wire size, even with 220VAC functionality indicates that it doesn't output a signal with much power. And there is no indication of what the output signal is like.

    In sum, research and design are up to you. Obviously, this does not involve Parallax products or even remotely a microcontroller. Please read the Forum guidelines about participation.
  • mac44mac44 Posts: 10
    edited 2014-12-31 01:56
    I already have the proximity switch and the motor is a 220v 3/4 hp rated at 9amps. The prox switch will only control the relay so output power is minimal.

    Thank you for your help and input.
  • tonyp12tonyp12 Posts: 1,951
    edited 2014-12-31 09:07
    In USA 220v is Black and Red wire Two Phase System (in Europe one wire alone is 220v)
    They both have 110V out of phase of each other to create the higher voltage.
    You also have a Neutral White wire that with either one of the above can be used to create 110V ac

    And then there is Ground/Earth green/bare wire, though Neutral is same as Ground they should only meet at main box. Ground should not be substituted for a Neutral wire.

    With 2 phase motor I would use a two pole relay to shut off both L1 & L2, adds some safety.

    Most USA homes have 2phase+neutral coming in to the house, only a dryer and stove use both then the two phases are split up ~50/50 to create the 110v system.
    You can not tell what phase is used for what part of the house as it uses black wire from both from here on.
  • LoopyBytelooseLoopyByteloose Posts: 12,537
    edited 2014-12-31 21:22
    It may seem as if I am intentionally holding back on a known solution, but the truth is that I only have a theoretical knowledge of switching 3/4HP AC motors. 9 amps at 220VAC is over 1800 watts of power, enough to nicely heat a small room.

    The issue of inductive loads comes into play with the switching. And so do both appropriate wire sizing for high amps and adequate insulation for high load in the actual context. When you combine all that with the general public trying to save money by going for the least costly solution, there just is little upside to helping out by discussing theory or what might apply in one locality (when the OP may be in another).

    The OP desires an actual reliable working solution. Someone knowledgible in his/her locality is the best authority.
  • 4x5n4x5n Posts: 745
    edited 2015-01-01 14:19
    kwinn wrote: »
    You can connect it between Neutral and either L1 or L2 as shown in the attached diagram. The relay coil should NOT be connected to ground. The motor case should be grounded unless it is double insulated and has a plastic case.

    RELAY CONNECTION.jpg

    I have major issues with the drawing you provided. At the very least BOTH L1 AND L2 need to be disconnected by the relay!! Think about it if the motor is powered off by the relay than when the relay is open 110VAC to neutral or ground at all times. This could get someone killed!
  • mac44mac44 Posts: 10
    edited 2015-01-01 23:47
    Thanks Tony!
  • mac44mac44 Posts: 10
    edited 2015-01-01 23:49
    4x5n wrote: »
    I have major issues with the drawing you provided. At the very least BOTH L1 AND L2 need to be disconnected by the relay!! Think about it if the motor is powered off by the relay than when the relay is open 110VAC to neutral or ground at all times. This could get someone killed!

    This is how the electricians wired it. The only difference is the one L1 is connected to a micro switch which is what I am replacing. It is by code!
  • LoopyBytelooseLoopyByteloose Posts: 12,537
    edited 2015-01-03 04:14
    This issue of 'by the code' is awkward as 'by the code' varies widely with location.

    Agricultural and rural electrical codes tend to be less stringent that the same in a large urban area. Farm buildings might be completely exempt from permits and inspection.

    And definitely Taiwan - with primarily concrete dwellings - does not apply the same code as San Francisco, California does.

    Even in the USA, there are substantial differences by state. In Oregon, I was permitted to completely wire and plumb my own home as long as I took out proper permits and did all the inspections. But in California, I doubt if a homeowner would be legally allowed to do anything unless a licensed plumber or licensed electrician supervised and signed off as responsible for the work. (Only those with plumbers or electricians in their immediate family might get buy without a hefty fee.)

    As far as safety with 220VAC, it is far safer to switch both sides as there is no hot and ground as in 110VAC. Both sides are hot unless both sides are disconnected. With just switching one side, even an off appliance can provide a serious 220VAC jolt to a person that thinks they have a full disconnect. You may be setting up an accident waiting to happen scenario.

    I have developed my own standards of safety for DIY and they may be higher than a local electrical code (certainly are higher than Taiwan's). You might consider developing your own. For instance, I prefer to use a metal box that is grounded for all connection boxes -- even though a lot of locations now use of certain plastic boxes. If there is a short or failure at a connection, this contains any hazard -- shock or fire. That's just one example. There are a lot of specifics, including how many connections can be placed within so many cubic inches in a box, grounding procedures, proper conduit, and on and on.

    Some locations still allow the use of aluminum wire instead of copper wire, but I consider it junk and hazardous. From what I understand, a lot of mobile homes have been wired with aluminum and this may contribute to a higher fire fatality rate -- junctions oxide and fail in a very hot manner, even with preventative measures.
  • PJAllenPJAllen Banned Posts: 5,065
    edited 2015-01-03 06:51
    I have developed my own standards of safety for DIY and they may be higher than a local electrical code (certainly are higher than Taiwan's). You might consider developing your own.

    Well then - there you go!
    You have developed your own so-called "standards" and mac44 has developed his.

    Leave the guy alone.
  • kwinnkwinn Posts: 8,697
    edited 2015-01-03 07:27
    mac44 wrote: »
    so if I connect to neutral instead of ground, the way I have it drawn will work?

    Sorry mac44, lost track of this post. Yes, it will work as drawn if connected to neutral instead of ground.
  • kwinnkwinn Posts: 8,697
    edited 2015-01-03 07:38
    4x5n wrote: »
    I have major issues with the drawing you provided. At the very least BOTH L1 AND L2 need to be disconnected by the relay!! Think about it if the motor is powered off by the relay than when the relay is open 110VAC to neutral or ground at all times. This could get someone killed!

    I agree. On the other hand, there is a lot of equipment in the field that is wired like that so anyone working on it should never assume that all power is off simply because a switch is in the off position. Always turn equipment off at the breaker panel and lock it out. Always make sure that equipment powered by 2 or 3 phases uses an appropriate 2 or 3 phase circuit breaker.
  • PJAllenPJAllen Banned Posts: 5,065
    edited 2015-01-03 08:33
    A switch, if it is supposed to de-energize a circuit, only de-energizes the circuit that it switches.
    That's all.

    The forum odometer hasn't tripped my account into "VIP" status.
  • tonyp12tonyp12 Posts: 1,951
    edited 2015-01-03 09:12
    >A switch, if it is supposed to de-energize a circuit, only de-energizes the circuit that it switches.
    In a 110V circuit you would never put the relay on the neutral return, though it will stop the motor from running and work as intended.
    On a 2-phase, both wires are hot and switching either one stops the motor from running, with a proximity switch of course no one would ever think the system is guaranteed off and do some work on the motor wiring.
    If you plan to replace the relay, get a two-pole one.
  • PJAllenPJAllen Banned Posts: 5,065
    edited 2015-01-03 09:57
    tonyp12,
    In such a matter as this, nobody should assume anything.
    I think that you are deliberately trying to change the subject.
    Be that as it may, I do object to your association of my post with your straw-man argument.
  • 4x5n4x5n Posts: 745
    edited 2015-01-03 16:13
    Can we please let this flame war end? I don't care who started it, who got the latest dig in, etc, etc! Just let it drop!
  • LoopyBytelooseLoopyByteloose Posts: 12,537
    edited 2015-01-04 04:27
    PJ Allen wrote: »
    Well then - there you go!
    You have developed your own so-called "standards" and mac44 has developed his.

    Leave the guy alone.

    I suppose I should have said 'higher standards of safety and durablity'.

    I am not so interested in evolking 'electrical code' or 'electrician only projects'. Neither is really a clear guideline on how to be safe.

    But the issues of safety and liability for offering advice over the internet come into play with switching AC main and inductive motors that are pulling serious power.

    Sorry about the flame war. I do admit that I can be a bit pedantic about safety, but that actually might not be such a bad thing.
  • GenetixGenetix Posts: 1,754
    edited 2015-01-04 14:15
    Mac44, I think Idbruce mentioned he was an electrician so I hope he chimes in on this thread.

    PJ, getting this thread locked is of no benefit to the OP (Original Poster).