I'm switching to a different forum for this question. My previous questions have been more Basic Stamp and ulc2003 related.

So here it goes.

I'm making a outlet box where the outlets can be controled by a micro controller via a ulc2003. So I'm going to use battery powered SSR's (already have several) to control the VAC outlet. One SSR per outlet. But, I also want this, a wall style switch that will bypass both SSRs and power the outlets ON. Right now I'm just making a simple 2 outlet box in a 3-gang/device metal junction box. So one section for the (2) outlets, one switch, and one place for the (2) SSRs to be inside.

My first thoughts were to buy a double-pole, double-through wall switch. HAH! Not only I haven't seen such in any hardware stores, but they are like $100 online. One pole for powering the outlet through the SSR(s) and the other pole to bypass the SSR and power the outlet directly. Doubt throw, one throw per each SSR/outlet set. But $100 is out of the question.

Now, I can find switches, (2) ganged one above the other, on the same switch plate, but they are only single-pole.

So here is the question. Is it harmful (to the SSR) to have a SPST switch bypass the contacts of the SSR? In other words when the switch is in the bypass mode, it would end up applying power to both VAC contacts of the SSR. Is that bad for the SSR? If not, it seems the simplist way to do it. If it's harmful then I have to keep searching for other double-pole switch solutions.

Hope this makes sense an I sometimes have difficulty wording my questions.

Henry

Comments

  • Mike GreenMike Green Posts: 23,101
    edited 2013-04-18 14:22
    No problem doing what you want. Unless the SPST switch is defective, it will have a very low resistance when it's closed, nothing that would affect the SSR.
  • frank freedmanfrank freedman Posts: 1,983
    edited 2013-04-18 17:33
    Mike Green wrote: »
    No problem doing what you want. Unless the SPST switch is defective, it will have a very low resistance when it's closed, nothing that would affect the SSR.

    Like Mike said, no issues. Heck, even if the switch fails open dumping the full line voltage across the SSR output pins, you will still have no more across them than you would in normal operation with the SSR in the off mode. Consider if you have not already, appropriate snubber ckts to protect the SSRs if feeding inductive loads.

    On the safety side of things though, make sure you are very careful of the clearances in your box and also ground anything that can be grounded that you or anyone else could come into contact with. Sure you don't want to go with a plastic or insulated box for this one?

    FF
  • Hal AlbachHal Albach Posts: 747
    edited 2013-04-18 17:37
    Could you not simply use the switch to turn on the SSRs through some diodes? Also, Since you are working with line voltages I strongly suggest including an indicator lamp to show that the outlets are "hot" as do the newer GFI outlets. This way if the outlet is under MCU control you will have an easy indication of the outlet status.
  • henrytjhenrytj Posts: 90
    edited 2013-04-18 19:00
    Like Mike said, no issues. Heck, even if the switch fails open dumping the full line voltage across the SSR output pins, you will still have no more across them than you would in normal operation with the SSR in the off mode. Consider if you have not already, appropriate snubber ckts to protect the SSRs if feeding inductive loads.

    On the safety side of things though, make sure you are very careful of the clearances in your box and also ground anything that can be grounded that you or anyone else could come into contact with. Sure you don't want to go with a plastic or insulated box for this one?

    FF

    Thanks. Yes, I intend to ground everything. The outlet box is being made to experiment with movie lighting effects. I want to be able to plug in (2) movie lights (max 1KW) per outlet. The switches are to test, and "warm up" the lights before the take. Then the SSRs, controlled by a Basic Stamp, will flicker to see if I can get a "Lightning" (or other, like welding, etc) effects. I was thinking that the SSRs (bottom metal plate) would be attached to the bottom of the metal outlet box to act as a heat sink. Maybe I'm wrong about that idea. The current shouldn't be flowing through the SSRs for more than a minute at a time. But, through the bypass switch, the lights might be on for a while.
  • henrytjhenrytj Posts: 90
    edited 2013-04-18 19:06
    Hal Albach wrote: »
    Could you not simply use the switch to turn on the SSRs through some diodes? Also, Since you are working with line voltages I strongly suggest including an indicator lamp to show that the outlets are "hot" as do the newer GFI outlets. This way if the outlet is under MCU control you will have an easy indication of the outlet status.

    That's an idea. So is the indicators. But for this first test (to see if the idea to simulate Lightning, ect with movie lights) even works. If it works, a better featured outlet box can be constructed. I figure (2) outlets with a light on each, would allow to see if the effect works. Lightning often has multiple cloud to cloud discharges associated with the primary bright lightning strike.

    I'm even wondering if a final box should also have it's own circuit breaker in case someone plugs in too high wattage of a light.

    Thanks again.
    Henry
  • henrytjhenrytj Posts: 90
    edited 2013-04-18 19:08
    I'm going to be testing this idea out on several different forms of lighting from tungsten filament, to quartz, to florescent, to maybe LED panels too.
  • frank freedmanfrank freedman Posts: 1,983
    edited 2013-04-18 22:27
    henrytj wrote: »
    I was thinking that the SSRs (bottom metal plate) would be attached to the bottom of the metal outlet box to act as a heat sink..
    Not sure I like the idea of a grounded metal box and the (potentially in failure) metal surface of the active device in direct contact. Good way to heatsink the things, but there are some good insulators with good thermal transfer characteristics I have seen used in High power/voltage supplies, they look like little gray silicone rubber strips. At best a failure metal to metal could blow the fuses or breakers, but if you ever have a ground open up on the box, a device failure could prove lethal. And we all know roadies and other equipment engineers religiously perform grounding and safety testing. Oh, your hair is just naturally curly?! Oh, check NFPA, UL, NEC for some good info on electrical safety information.
  • LoopyBytelooseLoopyByteloose Posts: 12,537
    edited 2013-04-19 02:27
    SSRs have gotten smaller and smaller and run cooler, so you might be able to build something that doesn't require a hockey puck sized SSR with a big heat sink.

    Regarding your switching scheme. ...
    The two choices are to have the 120VAC mains switched with a by-pass switch. Or to switch on the low volage side of the relay.

    The advantage of switching the 120VAC mains side is that you can completely bypass any failure of the unit and verify the rest of the circuit is operating correctly.

    The advantage of switching on the low voltage side is if you want to have your over-ride switches in a bank at the end of a cable that is some distance away from the SSRs and the mains wiring. It is always safer to run extension cords and cables as low voltage devices.

    I'd be more concerned about a good set of fuses or circuit breakers before I got into metal boxes and grounding. With the tiny SSRs that are available these days, you won't have any heat sinks, you might build in an all plastic box, and skip grounding the box entirely.
  • henrytjhenrytj Posts: 90
    edited 2013-04-19 15:15
    Thanks to the last two posters. And everyone else as well.

    Okay, rethinking the metal box idea. I had sent all this to my EE relative, but they have yet to get back to me. I expect that his comment might be the same. It's just that he's a busy person with job (travel) and family. I, on the other hand, am unemployed, and have what some might consider too much time. Though I do have 7 short stories currently out, two screenplays up on a review site, and planning a video for a Kickstarter project. So, I'm actually more busy than when I'm working.

    Thanks. All the advice is being absorbed and processed.
    Henry
  • henrytjhenrytj Posts: 90
    edited 2013-04-19 15:18
    I guess why I thought of a metal box was because when I was back taking film school courses (30 years ago) the equipment office had extension cords that were essentially long heavy 3 wire cords with 4-outlet metal outlet boxes at the end. So was just thinking of those.
  • LoopyBytelooseLoopyByteloose Posts: 12,537
    edited 2013-04-20 02:17
    Yes, three or more decades ago... everything that had 120VAC or higher was put in an electrical box with a ground. The idea was simple. Contain any failure and fire hazard to a metal box. But in some cases, the ground actually becomes an additional failure hazard. And now we have plastics that will not burn.

    I do admit that a lot of plastic boxes available still can burn with toxic fumes. But if the connections are good and the devices are reasonable, they do work well.

    Theatrical wiring is especially aware of fire hazards as you have hundreds of people attending an event and any fire can create a panic far beyond the realities of the fire hazard.
  • henrytjhenrytj Posts: 90
    edited 2013-04-20 11:58
    Thanks. In looking around I've seen some fiberglass electrical boxes. The glass itself isn't flammable, but I don't know about the resin. Anyway, sounds like the way to go.

    Thanks,
    Henry
  • frank freedmanfrank freedman Posts: 1,983
    edited 2013-04-20 15:25
    In addition to NFPA 70(NEC), check out also NFPA 140 which is specific to your end uses.
  • evanhevanh Posts: 15,948
    edited 2013-04-22 14:52
    The heat pad, bottom metal plate, on a typical block shaped SSR is isolated. So, as long as the metal outlet box is earthed with an actual earth wire then it's electrically safe to use the outlet box for heat-sinking the SSR.

    However, adding heat stress to the outlet box might be another cause for concern. Is there ventilation inside the wall?


    PS: Regarding the earth wire being a fire hazard, that would only be true if not wired correctly. In normal use the current in an earth wire will be below a few milliamps of leakage. In a fault condition the earth wire can carry the fault for the few milliseconds it takes for the circuit-breaker or fuse to trip. Modern homes are additionally wired with an earth leakage breaker so that the leakage can't be above 30 mA I think it is.
  • frank freedmanfrank freedman Posts: 1,983
    edited 2013-04-22 20:07
    But, be a aware that per code, GFCI is normally required only in damp/wet areas such as kitchens and bathrooms or pool areas. All else will be just standard unprotected (other than breaker/fuses) outlets.
  • evanhevanh Posts: 15,948
    edited 2013-04-23 05:03
    Country dependent I guess.
  • frank freedmanfrank freedman Posts: 1,983
    edited 2013-04-23 16:13
    Worse actually, NEC, state, county, city and who trumps whom in any given local is anyone's guess. Not to mention the fees, fines, and permits.......
  • evanhevanh Posts: 15,948
    edited 2013-04-24 03:57
    I was referring to normal practice of covering the whole house by earth leakage breakers at the distribution board.