4-20ma current loop question
xanatos
Posts: 1,120
OK, so I have a PLC designed to receive a 4-20ma current loop signal. 20ma = highest point, 4ma = lowest point. The specs say it's a 24volt system. But when I put 24 v across the 250 ohm PLC load, of course I would get a lot more than 20ma.
For example, if I was to put 24v into 250 ohms, I would get 96 ma (I=V/R = 24/250 = 0.096A)
To get 20ma into a 250 ohm load, I would really need 5V plus the V drop of the loop, correct?
Why do they spec it as a 24v system?
Thanks for disconfuzzlating me,
Dave
For example, if I was to put 24v into 250 ohms, I would get 96 ma (I=V/R = 24/250 = 0.096A)
To get 20ma into a 250 ohm load, I would really need 5V plus the V drop of the loop, correct?
Why do they spec it as a 24v system?
Thanks for disconfuzzlating me,
Dave
Comments
-Phil
Thanks!
It starts to enter limiting at less than 20mA, as Q2 starts to turn on and robs the base of Q1, and is fully limiting at about 25mA. The transistors are inside the feedback loop that regulates the loop current.