bs2 4-20ma
What is the best way to get a value on a bs2 from a transducer with a 4-20ma output? I have a ad converter working with a 1-6 volt output transducer, what is your plan?
Thanks, Toby
Thanks, Toby
Tracy Allen
www.emesystems.com
Thanks, Toby
This is for a loop powered transducer. Some transducers have their own power supply and simply produce the 4-20 mA on a pair of output wires.
Tracy Allen
www.emesystems.com
Thanks, Toby
You are probably correct. That is a typical 3-wire 4--20 circuit. If you use 150 Ohms, the output voltage will be 0.6--3.0 V. With 250 Ohms, it will be 1--5 V.
Tracy Allen
www.emesystems.com
Thanks, Toby
If it is a separately powered transducer:
Tracy Allen
www.emesystems.com
If you have three wires, they will (probably) be power, signal and common. In that case follow the second diagram above with the 250 Ohm resistor and the signal output wire is the point "A" in the diagram. You use your voltmeter or Stamp with ADC to measure the voltage across the resistor. The resistor converts V = I * 250, that is, 4-20 mA to 1-5 Volts. It is really quite simple!
Tracy Allen
www.emesystems.com
I work with 4-20ma Transmitters all day long.What Tracy Allen suggested should work.
Some transmitters will only take so much current.Adding and another 250 ohm resister might help.
Is Your transmitter smart? Hart,MODBUS,etc.
Do You have some specs for Your Transmitter?
The Truth is out there············___$WMc%___···························· BoogerWoods, FL. USA
