Proper way to drive a 24VAC solenoid?
![CounterRotatingProps](https://forums.parallax.com/uploads/userpics/360/nWQG6ZTFJSJXM.png)
Hi All,
Picture·a 24V AC sprinkler-valve control solenoid and you'll know what I've got here on the bench.
It has about 400mA surge at pull-in and about 120 mA run.
It may toggle on/off·upwards of 50 times per day and needs to run like this for, preferably, years. (They can do so·with 24VAC relay.)
I'd like to control them with an SX or B.Stamp.
Was thinking of PINOUT to a driver/buffer transistor·then gating a properly rated triac.
Is that overkill ?
Is there a simpler way ?
What would you recommend to avoid inductive coil kick-back ?
thanks so much for your time!
Howard
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
No matter how much you push the envelope, it'll still be stationery.
Picture·a 24V AC sprinkler-valve control solenoid and you'll know what I've got here on the bench.
It has about 400mA surge at pull-in and about 120 mA run.
It may toggle on/off·upwards of 50 times per day and needs to run like this for, preferably, years. (They can do so·with 24VAC relay.)
I'd like to control them with an SX or B.Stamp.
Was thinking of PINOUT to a driver/buffer transistor·then gating a properly rated triac.
Is that overkill ?
Is there a simpler way ?
What would you recommend to avoid inductive coil kick-back ?
thanks so much for your time!
Howard
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
No matter how much you push the envelope, it'll still be stationery.
Comments
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
propmod_us are now in stock. propmod_1x1 arrive on 26th. Only $30
Need to upload large images or movies for use in the forum. you can do so at uploader.propmodule.com for free.
-Phil
Leon
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
Amateur radio callsign: G1HSM
Suzuki SV1000S motorcycle
kwinn's suggestion seems the best option because it has all the parameters you all have suggested - and the moc3030 is $6 - certainly cheaper than an SSR.·· But kwinn, you probably mean driving a triac?
That said, I was thinking about SSR's for another application... but...
It's been literally decades since I"ve used an SSR. Back then we put a cap across either the load or trigger --- but I can't recall which (I smell smoke [noparse]:)[/noparse] --- but it was for snubbing I think. (I can image that the manufacturers realized the oversight and put these inside.)
Phil, do the built in snubbers make this unneed?
thanks again·!
- H
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
No matter how much you push the envelope, it'll still be stationery.
Post Edited (CounterRotatingProps) : 5/25/2009 10:05:35 PM GMT
The 70M-OAC5 is $9.50 from Digikey. Part Number GH7022-ND
A few more $ but you get a 140 VAC 3 Amp Triac with the snubber built in.
The MOC3030 is rated at 1 amp and has no snubber.
You can connect it directly to a Stamp pin.
You need to look at the cost of a part failure in your dsecision.
Is it worth saving $3 when the solenoid stays on due to a shorted triac.
Will this flood a lawn, drain a well, fill a basement, run up a $500 water bill, etc.
The data sheet on the MOC3030 says it is rated at 100 MA with 1.2 Amps peak.
If it takes 400 ma to pull in the solenoid, what is the holding current?
This is not enough to reliably run your solenoid. This is a maximum or higher load.
You also need to derate the chip as it gets warmer.
A 3 Amp SSR is less likely to fail than a .1 Amp Dip chip Triac.
You will be running it ar about 15% of its maximum rating.
It seems worth the extra $3 to me.
I have attached a copy of my StamPLC that uses 16 SSIO modules.
We have installed around 100 of thesedriving 120 VAC Gas/Water Solenoids,(the same ratings as your solenoid)·and have not had a failure yet.
Hope this helps you out.
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
Alan Bradford
Plasma Technologies
Canaan NH 03741
www.plasmatechnologies.com
Alan and kwinn,
thanks for answering my next questions - before I asked them. ( Ever heard of Psychic Pizza ? It's guaranteed delivered five minutes before you think of ordering [noparse]:)[/noparse]
Very cool, last time I used SSR's they were really expensive - but how can you beat <$10 ? The solenoids are 400 mA pull and about 200mA run (at least that's how they're labeled) so the Grayhill device will certainly have plenty of headroom.
Thanks a lot, Alan, for the pdf - yes, it will decidedly be helpful in many ways - I'll study it carefully.
Taking a related tangent here a second...
Kwinn, that zero crossing detection implies that snubbing is unnecessary helps clarify what snubbing _really_ does. (I've always considered snubbing, shunting, esi, esd
- and lightning-rods! amoung the Grey Arts.)
It's just basically the reverse of current, the collapse of the coils mag. field, and the resulting kick back that needs to be snubbed out, right?
So, at zero crossing, the flow goes to zero and *shazam* no kick back - at that instant?
But, as my 12 year old nephew (and I) wonder, AS it is crosses zero, where does the coil's discharge actually go ?? Into itself? Into Some Alley in New Jersey?
And really basic here:
Is the term "Snubbing" properly used only for A.C. (Or A.C.-like)?
and "Shunting" only to D.C. (Or D.C. like)?
thanks
- Howard
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
No matter how much you push the envelope, it'll still be stationery.
I guess the old SSR's·didn't have zero crossing detectors ... I recall if we left off the cap., they'd zonk out after a while. Pretty good guesses!
In my case, failing part would·result in: "run the well dry and have tenants complaining that their A.C. isn't cooling."
Avoiding that is worth almost $300 !·· So thanks again for the bargain, Alan!
- Howard in Florida
~~~~~~~~~~~~
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔