IO Line Distance
Hi all
Plan on doing an experiment but thought i would ask firt.
What is the max cable distance a bs2 or sx chip drive a 2n222 transistor.
I want to use a 20 IO sx chip to drive my christmas lights.
But i want to seperate it into modules.
Each Module having 4-5 IO's and spaced up to 10 meters away from the microcontrollers.
Thoughts??
Thoughts??
The "Ohms per 1000ft" can be looked up for your wire size based on National Electrical Code tables.
For You will find a table like this:
AWG Dia-mils TPI Dia-mm Circ-mils Ohms/Kft Ft/Ohm Ft/Lb Ohms/Lb Lb/Kft *Amps MaxAmps
20 31.961 31.288 0.8118 1021.5 10.153 98.496 323.41 3.2832 3.0921 1.3620 2.0430
21 28.462 35.134 0.7229 810.10 12.802 78.111 407.81 5.2205 2.4521 1.0801 1.6202
22 25.346 39.453 0.6438 642.44 16.143 61.945 514.23 8.3009 1.9446 0.8566 1.2849
23 22.572 44.304 0.5733 509.48 20.356 49.125 648.44 13.199 1.5422 0.6793 1.0190
24 20.101 49.750 0.5106 404.03 25.669 38.958 817.66 20.987 1.2230 0.5387 0.8081
25 17.900 55.866 0.4547 320.41 32.368 30.895 1031.1 33.371 0.9699 0.4272 0.6408
26 15.940 62.733 0.4049 254.10 40.815 24.501 1300.1 53.061 0.7692 0.3388 0.5082
27 14.195 70.445 0.3606 201.51 51.467 19.430 1639.4 84.371 0.6100 0.2687 0.4030
28 12.641 79.105 0.3211 159.80 64.898 15.409 2067.3 134.15 0.4837 0.2131 0.3196
29 11.257 88.830 0.2859 126.73 81.835 12.220 2606.8 213.31 0.3836 0.1690 0.2535
Lets say you used 22 AWG Phone Hookup Wire... from the table, at a 1000ft that would be 16.143 ohms.
Lets say you are being nice to your 2N2222 and using a max of 500Ma, 33ft at 5.0V
Vd = 2*R*L*I/1000
where:
Vd = Voltage drop
R = DC Resistance from NEC® Chapter 9 Table 8 (see above)
L = Distance
I = Current in amperes (A)
At 33Ft, the voltage drop is close to 0.55 volts, resulting in 4.45V where you expect 5.0.
Pete
There's nothing like a new idea and a warm soldering iron.