Here is what i want to do
So feet and hands are not where the· Equipment··can hurt you
I want to use two switch that are depend on each other with two inputs to a Basic Stamp and ..........
Which Basic Stamp would be the Right choice and why ???
I want it so that each switch has to make with in a second of each other to be·valid
other wise lock out is in forced and you must start again
I am just looking for ·
·s for now
Where·I work at we are having trouble with this· piece of Equipment·and the cost of this board is $1500
it also dose other functions besides the one i have here
One this that is bad with this setup is that it send 120 volt to the switch for safety switches
Both Switch Must make with in ONE Second
Switch 1
Switch 2
If not then both switchs must be released and start over
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
··Thanks for any·
·that you may have and all of your time finding them
·
·
·
·
Sam
Post Edited (sam_sam_sam) : 9/30/2008 1:38:07 AM GMT
So feet and hands are not where the· Equipment··can hurt you
I want to use two switch that are depend on each other with two inputs to a Basic Stamp and ..........
Which Basic Stamp would be the Right choice and why ???
I want it so that each switch has to make with in a second of each other to be·valid
other wise lock out is in forced and you must start again
I am just looking for ·
![idea.gif](http://forums.parallax.com/images/smilies/idea.gif)
Where·I work at we are having trouble with this· piece of Equipment·and the cost of this board is $1500
it also dose other functions besides the one i have here
One this that is bad with this setup is that it send 120 volt to the switch for safety switches
Both Switch Must make with in ONE Second
Switch 1
Switch 2
If not then both switchs must be released and start over
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
··Thanks for any·
![idea.gif](http://forums.parallax.com/images/smilies/idea.gif)
·
·
·
·
Sam
Post Edited (sam_sam_sam) : 9/30/2008 1:38:07 AM GMT
Comments
What is the specification of the output when a sucessful two switch sequence is made?·
There may also be simpler ways to accomplish your goal.
If this is just to ensure that it takes two hands to activate thus ensureing that both hands are not in/on the equipment. Why not just put two N.O. momentary switches in series and mount them about 1 foot apart from each other?
You could also make the curcuit you descript with a a few simple components like an RC circuit that closes a releay. If both switches are pressed before the releay closes then you activate the equipment. If not, then you have to wait for capacitor to discharge.
Also look at LM555 timers.
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
Searider
Thank You for your reply
I have to ask you something
You could also make the circuit you descried with a a few simple components like an RC circuit that closes a relay.
How would do this set up with capacitor and two relays
If both switches are pressed before the relay closes then you activate the equipment.
If not, then you have to wait for capacitor to discharge.
·
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
··Thanks for any·
·
·
·
·
Sam
http://hyperphysics.phy-astr.gsu.edu/hbase/Electronic/and.html
If the timer is necessary, you could run an additional output from each switch to the stamp, and start a conditional timer loop that has to be met before the and output would become active. So the stamp would wait for button press 1, it starts a 1 second timer waiting for button press 2, if not, go back and wait again for button 1. If condition is met, then allow input from and gate / output from stamp to be sent to machine.
Post Edited (kelvin james) : 10/4/2008 4:51:43 PM GMT
However, you can work with your Dept of Labour inspector and get him/her to help you test and accept the modifications.
More complicated procedure to be sure, but the owner of the business will thank you in the long run.
The issue is that the two buttton system must also reject a scenario where the operator ties down one button. These circuits
are also called "anti-tie-down" circuits for that reason.
Cheers,
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
Tom Sisk
http://www.siskconsult.com
·
I had not thought of this part I am gald that you brought this up and thank you for it
Tom Sisk
However, you can work with your Dept of Labor inspector and get him/her to help you test and accept the modifications.
More complicated procedure to be sure, but the owner of the business will thank you in the long run.
This one thing I was going to add to it which it dose not have now
The issue is that the two button system must also reject a scenario where the operator ties down one button. These circuits
are also called "anti-tie-down" circuits for that reason.
▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔▔
··Thanks for any·
·
·
·
·
Sam
It is perhaps more an exercise in failure mode analysis than anything else. Consider one potential fault - the switch has become disconnected and the input is floating and appearing to flip high and low; pressing just the one switch in those circumstances could lead to a false recognition of valid trigger.