Reactive Power Calculations
Hi,
Let's say I have a 1uf 400V capacitor in series with a 10ohm resistor.
If I connect this pair directly to AC 240v 50Hz supply, how many watts would it consume?
www.fd.com.my
www.mercedes.com.my
www.fd.com.my
www.mercedes.com.my
1 / (2 * pi * f * C)
where: 2 * pi = 6.2832; f = frequency in hertz and C = capacitance in Farads
then simple ohms law for the two series resistances will give Current and from that Power
3183+10 = 3193 ohms
I =V/R·· 240/3193 = 0.075 amps
P=VI· 240*0.075 = 18W - wrong should use P=I2R here instead which gives 0.05W not 18W
I think that's right but double check my calcs as i am rather tired at the moment
Post Edited (skylight) : 8/23/2008 9:10:11 PM GMT
At that frequency, the impedance of the cap will dominate and appear as about 3.14K·
That will limit current to about·76 mA. Note that your capacitor voltage rating is, IMHO, marginal for 240 VAC service.
Cheers,
<< edit for slipped decimal>>
Tom Sisk
http://www.siskconsult.com
Post Edited (stamptrol) : 8/23/2008 9:51:56 PM GMT
According to the simulator, the resistor will consume about 57 milli-Watts, while the capacitor will consume about 9 Watts
www.falstad.com/circuit/
Beau Schwabe
IC Layout Engineer
Post Edited (Beau Schwabe (Parallax)) : 8/23/2008 4:08:55 PM GMT
Yeah, looks like that site has poor bandwidth right now.... I just downloaded the stand-alone version (no internet required) ... www.falstad.com/circuit/circuit.zip
Once the applet loads, go to "File" --> "Import", and then paste the code into the window .... then click "Import"
Beau Schwabe
IC Layout Engineer
http://www.opamplabs.com/rfc.htm
1uf at 50 Hz comes out at 3183 ohms as in my post above, adding the 10 ohms,with ohms law this comes out at 18watts total power
Post Edited (skylight) : 8/23/2008 4:28:41 PM GMT
Z = (R2 + X2)1/2
Post Edit -- Here's a better calculator: http://pr.erau.edu/~newmana/imped.html
The answer is Z = 3183Ω
Post Edited (PJ Allen) : 8/23/2008 4:58:59 PM GMT
the AC reactance part of the circuit is taken care of with the Xc formula.
I know you are going to say X= XL-Xc
Where is the inductance in the circuit? we are talking a capacitor and resistor here no coils or such (unless you are talking of minute inductance in practice that the resistor may show, if so then if we were talking about uA it may make a difference but at the magnitudes we are discussing its negligible and can be ignored).
The impedance of an RC circuit is not the arithmetic sum of the capacitive reactance and resistance.· Why?· Because it's a reactive circuit, all of it, the R and the C, the R and the XC.
You ought to take a look at the old texts or do some research ("wiki that.")
Z=sqrt ((10*10)+(3183*3183))
Z=sqrt (100)+(10131489)
Z=sqrt (10131589)
Z= 3183.0157084123854508841679646369 ohms
back where we started there is no inductance to worry about in this circuit so XL was ignored the formula above cancels out the squaring and square rooting so the resistance and reactance add together as i said before to give Z or impedance.
I agree if the inductance in the circuit was of significance then the formula above would come into play but not in this instance.
Beau calculated 9.057w.
If the capacitor is dissipating 9w, it would have been very hot after a while, but it is cool.
I think a joule meter would show a value less than 3w.
The reading from an actual joule meter is what is important to me.
www.fd.com.my
www.mercedes.com.my
its the reactive element the Xc which you were saying cannot be added to the 10 ohm resistance and i was arguing the point that as there is no inductance in the circuit to react·the Z formula you were quoting takes X which is actually XL-Xc as just being Xc and therefore Z can be taken as being Xc.
the above calculation proved it by not altering the Xc value of 3183 ohms,so·for this application the Z formula is simplified to Z=Xc.
Maybe the difference comes from two different backgrounds where you are arguing from an electronics viewpoint and i am from a power viewpoint as an electrician. the small inductance in an RC network would make a difference if say it was a filter in a preamp for instance where uAmp/mA currents flow and those tiny inductive elements·may well be·of importance, but the OP was talking of a mains circuit with higher voltages and currents where small is meaningless and for all intents and purposes can be ignored.
The calculation of the power is not simply P=VI because the voltage and current phases have been skewed by the reactive circuit.
www.fd.com.my
www.mercedes.com.my
In your opinion, what would be the joule meter reading?
www.fd.com.my
www.mercedes.com.my
Less than 1 joule.
www.fd.com.my
www.mercedes.com.my
www.fd.com.my
www.mercedes.com.my
·did say i was tired·
Post Edited (skylight) : 8/23/2008 9:10:54 PM GMT
The values that I gave rely purely on the simulator.... 10 Ohms, 1uF,·240V, ·50 Hz
This may shed some light...
http://hyperphysics.phy-astr.gsu.edu/Hbase/electric/powerac.html
http://hyperphysics.phy-astr.gsu.edu/Hbase/electric/acres.html#c2
"...Since the voltage and current are both sinusoidal, the power expression can be expressed in terms of the squares of sine or cosine functions, and the average of a sine or cosine squared over a whole period is = 1/2..."
Beau Schwabe
IC Layout Engineer
Post Edited (Beau Schwabe (Parallax)) : 8/23/2008 9:15:53 PM GMT
